Hi,
A surface (F_SPC) has been applied to all the surfaces of your mezzanine that releases linearly and up to 600 s a power per unit air of 4,000 kW/m2. Carrying out the calculations comes out with a very high peak HRR.
Assimilating the mezzanine to a parallelepiped we have:
Top side and bottom side= (4.40 m x 10.25 m) x 2 = 90.20 sq. m.
Short side= (4.40 m x 2.80 m) x 2= 24.64 sq m
Long side= (10.25 m x 2.80 m) = 57.40 sq m
Total Area= 172.24 sqm
Total HRR= 172.24 sq m x 4,000 kW/sq m = 688,960.0 kW
This represents a very large fire, and not comparable to your office fire in any way.
What you are calling the fuel load is the total amount of energy released when the fuel is burned. If you had a HRR curve, then the area under the curve would be the fuel load. In terms of units,
HRR (kJ/s) x Time (s) = Fuel Load (kJ)
So, if you have calculated the fuel load for a given room, you then have to decide how long it will take for it to burn.
Fuel Load (kJ) / Time (s) = HRR (kJ/s = kW)
The cell size is usually a function of the HRR or according to the sensitivity you want to achieve. There are relationships that on the basis of the power released allow you to estimate the mesh size.
If your structural elements (beams, pillars, walls, etc...) do not fill the whole cell it does nothing, via surface you can imost the thickness value and tell FDS to consider a smaller size.
Finally, I think you need to model the loft openings, perhaps as holes, simulating the worst-case situation, i.e., open doors and windows. Evaluate whether as a result of the fire your fumes are hot enough to propagate the fire to the ground floor.
dr_jfloyd please correct me if I said something wrong.
Have a nice day