Hi,
I'm working with a case with beam detectors over a large area meaning
that several meshes must be used. Problem is that beam detectors
cannot cross mesh boarders. So I came up with a solution that i think
is correct, throwing it in here for anyone to have their say.
I first determined the point where the beam is cut in the mesh
boarder. Then made a new beam stretching from that point to my end
point, a simple example below:
&HEAD CHID='linje3'/
&TIME T_END=120.00/
&DUMP RENDER_FILE='linje3.ge1', DT_DEVC=0.1000/
&MISC RADIATION=.FALSE./
&MESH ID='MESH', IJK=15,30,30, XB=0.00,1.50,0.00,3.00,0.00,3.00/
&MESH ID='MESH02', IJK=15,30,30, XB=1.50,3.00,0.00,3.00,0.00,3.00/
&SURF ID='Fire',
COLOR='RED',
HRRPUA=50.00/
&DEVC ID='BEAM', QUANTITY='path obscuration',
XB=0.00,1.50,1.50,1.50,2.50,2.50/
&DEVC ID='BEAM02', QUANTITY='path obscuration',
XB=1.50,3.00,1.50,1.50,2.50,2.50/
&OBST XB=0.1000,0.70,0.1000,0.70,0.00,0.1000, SURF_ID='INERT'/
Obstruction
&VENT SURF_ID='Fire', XB=0.1000,0.70,0.1000,0.70,0.1000,0.1000/ Vent
&TAIL /
In this case the first beam will go from x=0 to 1.5 and then x=1.5 to
3.0.
Then I started the calulations and after looked in the devc.csv.
To add up the two beams resulting in the same as if it was one beam in
one mesh i calculated the following:
B= -ln((1-"obscuration beam 1")/1)+(-ln((1-"obscuration beam 2")/1))
total obscuration = 1-e^(-B)
What I do is calculate the obscuration to optical density and then add
them together and transform it back to obscuration.
Did a couple of test runs and calculations comparing to a single beam
and mesh case (the one beam covering the same path as the two
together) and it seems to give approximately the same answer, small
differences do occur but i think this is due to small differences in
time steps.
Any comments or any other ideas to solve this problem? The bad thing
about this method is that when the beam detector is to activate a fire
vent for example, you have to do the simulation one time to get the
time to detection, and then another one with the fire vent activating
at this given time.
/Jonathan