HVAC Jet Fan Issue

337 views
Skip to first unread message

Chuma A

unread,
Feb 23, 2015, 10:28:45 AM2/23/15
to fds...@googlegroups.com
Hello,

I am new to FDS and have read the User's Guide.

I am trying to model a car park with jet fans. I have added 3 fans to the model at different points (all with the flow along the x-axis) and it has run successfully. However on adding another jet fan but with flow along the x-axis, I get the error message attached. This is the same code as in the FDS examples and I have always tweaked it to use, I do not comprehend why it isn't running now. The code is also attached (the error is with 'JET FAN13')

Chuma.
error_code.PNG
withjetfans.fds

dr_jfloyd

unread,
Feb 23, 2015, 10:47:43 AM2/23/15
to fds...@googlegroups.com
You have made the VENT color for the fans the same as the OBST they are attached to. This makes it hard to tell if the VENT's have been properly applied.  Make the VENT color different then look at the smokeview file to make sure your VENTs are being applied correctly. If you don't find an error that way, post a simplified version (get rid of everything that doesn't relate to the problem) of the file to the issue tracker.

Daniel Swenson

unread,
Feb 24, 2015, 1:23:38 PM2/24/15
to fds...@googlegroups.com
Chuma,

On line 5 you did not use the proper quote characters to define the ID. See the attached images.

The reason I read your question is that I am working on jet fans and wanted to see what problem you had.

Best wishes,
Dan
withjetfans problem on line 5.PNG
withjetfans error with quote characters.png

Chuma A

unread,
Feb 25, 2015, 3:36:32 AM2/25/15
to fds...@googlegroups.com
Hello Dan,

Thanks for the reply. I do not use Pyrosim, and FDS did not give an error message for the REAC line. It's probably a pyrosim construct.

Kind regards,
Chuma.

Andrew Louie

unread,
Feb 25, 2015, 9:23:11 AM2/25/15
to fds...@googlegroups.com
Your entire domain only goes from 0-3.4 meters in the Z direction,
each cell is 0.435m tall

Your JET FAN13 is specified from 3.2 to 3.5 meters putting part of the
jet fan outside your domain.

Also, you need to snap your coordinates to your grid: Specify the
coordinates of the VENT to be whole number multiples of your gird
resolution.
> --
> You received this message because you are subscribed to the Google Groups
> "FDS and Smokeview Discussions" group.
> To unsubscribe from this group and stop receiving emails from it, send an
> email to fds-smv+u...@googlegroups.com.
> To post to this group, send email to fds...@googlegroups.com.
> To view this discussion on the web visit
> https://groups.google.com/d/msgid/fds-smv/a80373a1-a615-43b3-bc30-be66f9a2cb6b%40googlegroups.com.
>
> For more options, visit https://groups.google.com/d/optout.



--
-Andrew Louie :wq

Chuma A

unread,
Feb 25, 2015, 10:54:35 AM2/25/15
to fds...@googlegroups.com
Thanks Andrew.

I didn't realise that. I was working with a different MESH beforehand.

Chuma.

Chuma A

unread,
Feb 25, 2015, 11:02:37 AM2/25/15
to fds...@googlegroups.com
Slightly new question, but on the same FDS model.

When the time-step does not change (after the first step, even though the code set-up properly), is that a sign that I need a machine with a higher processor? I have nine jet fans in the model now.