Only recently we've noticed the inverter getting remotely shut down by the SBMS during high load (for us that is a kettle). Then a few moments later the inverter turns back on again. This cycle may repeat a few times under load.
The system is around 80-90 % SOC
Upon investigation, with load, cell #1 is dropping to around 2.8 volts (which is the default low voltage cutoff). 2 or 3 other cells drop to about 3 volts under load. Cell #8 stays the highest.
We do not have spec sheets for these cells so I do not know the original C rate. However, the cells used to be able to handle these loads.
My assumption is the cell health has deteriorated and has reached end of life. Does it make sense to try to replace just cell 1? Or will that throw off the balance of our 8-cell system
Thanks,