There is no setting for round trip efficiency in the SBMS. I can implement that in a future update.
For typical solar energy storage applications using LiFePO4 the round trip efficiency is around 99% or higher.
In normal cases where you discharge say battery down to 40% over night and have a full charge the next day the SOC discrepancy will be less than 1%.
If you have a full week with not a full charge it will also likely mean that you where not able to use 60% of battery capacity every day maybe just an average of 20 or 30% with those partial charge cycles so maybe the SOC will be OFF by 2 or 3% and will get corrected when a full charge is made.
Of course if you operate for many weeks without a full charge for some reason you can get to significant SOC discrepancy. On the other hand if I implement the round trip efficiency and that value is introduced incorrectly it can create as large or even larger discrepancy.
With my own two SBMS units I never noticed more than 2 to 3% SOC discrepancy over the past few years. I only have periods in winter where there may be a few days up to around a week where I do not get a full charge.
You can get a way larger discrepancy if you have a bad cell connection or you charge with more than 0.2C since in this cases the cell due to internal resistance or extra resistance of a bad connection can get to the 3.55V limit way before cell is at actual 100% SOC. So you can get even a 20 or 30% SOC discrepancy in this conditions in just a single day. Same will happen if you set the over voltage limit to some lower value than default 3.55V.