My LiFePO4 Battery capacity test after 3 years

302 views
Skip to first unread message

Dacian Todea

unread,
Jul 16, 2020, 7:35:19 PM7/16/20
to electrodacus
I will add first the original test result as they where presented on google+ in 2017 and 2018 so is a copy paste as google decided to discontinue google+ hopefully the forum will last longer.


29.07.2017___________________________________________
I decided to do a capacity test on the new A123 System battery using the SBMS120 so what I did was to disconnect all PV panels about two days ago when the battery was fully charged and reset the energy counters and then just wait until the battery is empty and that happened today around 14:30 so still early enough to recharge the battery enough for what is needed tonight.
I took a few photos before I got to 0% SOC end even when at 0% I needed to wait a bit since I defined the battery as 180Ah in parameter settings but as you can see in last photo the usable capacity is slightly higher at around 188Ah (4.9kWh) and that had the lowest cell still around 3V under moderate load 35A
The default low voltage disconnect is set at 2.8V but I did not wanted to go there and there will not have been much extra energy in there anyway.
It is an extremely decent battery and love the very low internal resistance is just not something I can recommend to others because of the amount of work to build a pack out of this cells and the fact that they are from unknown sources (you can not just buy new cells from A123 so you get this not that great looking cells from unknown sources).

soc39.jpg

soc39-2.jpg

soc19.jpg

soc7.jpg

soc0.jpg

capacity1.jpg






29.07.2018___________________________________________________________________
Time for Battery capacity test.
There is about 1 year since I installed my A123 System battery that powers my entire offgrid house.
The photos are in the order they where taken so I started in the morning charging the battery even added a few more panels on PV2 to charge the battery faster and after the first time it went to 100% fully charged I disconected the panels on PV2 so charge current is lower and added a 25A DC load just to spped the discharge a bit so it will start charging again at around 10 to 12A then one more time before starting the discharge test.

My settings are 3.50V Over voltage so when the highest cell gets there the charging is stopped and End of Charge is set at 3.48V thus the charge re-enable voltage will be 130mV lower (fixed setting inside the ISL94203) so highest cell needed to drop to 3.35V before charging will start again as it seems there is about 2Ah between fully charged and when the charging is re-enabled thus for this battery just a bit over 1% SOC

Now battery is fully charged indication is 99% and PV are physically disconnected from SBMS120 so no more charging so test is started by resting the energy counters.

Now you can see how battery voltage will progress with highest cell voltage and delta to lowest cell as follow:
99% -- 3.458V -- 10mV (1.3A)
89% -- 3.288V -- 7mV (88A)
80% -- 3.286V -- 10mV (87A)
80% -- 3.303V -- 4mV (28A) (this is a few seconds later from above).
70% -- 3.263V -- 12mV (87A)
60% -- 3.263V -- 7mV (50A)
50% -- 3.257V -- 7mV (50A)
39% -- 3.249V -- 7mV (50A)
30% -- 3.230V -- 7mV (50A)
20% -- 3.205V -- 8mV (50A)
10% -- 3.170V -- 9mV (50A)
1% -- 3.108V -- 12mV (50A)
0% -- 2.998V -- 34mV (31A) (point where the test was stopped).

The entire discharge test took just a little bit less than 4h so average discharge current was around 48A (0.25C) with peak at 88A (0.5C) thus absolutely no trouble for this battery.

Now while at 3.5V this battery was actually fully charged (there is no capacity gain to go to 3.6V) on the lower end I stopped the discharge at about 3V so there was still something down to 2.8V but not much and official tests go down to 2.5V but again not much extra capacity to be had going there as voltage will drop fairly fast below 3V

Now to compare this with the initial test after installation made one year ago you need to read this old post here https://plus.google.com/+electrodacus/posts/ckVqrv2SCBL

That test was done a bit differently as after the cells where fully charged I disconnected the PV and continued normal house discharge usage and so the discharge test was about 2 days instead of just 4h for this test so average load was a bit lower so that test had a bit of an advantage over this one but not much.

If I ignore the difference in test procedure and possible small measurement tolerances and just compare the numbers then that test made a year ago resulted in a discharge capacity of 187.89Ah vs this test made today that had resulted in 186.22Ah then delta in capacity is 187.89Ah / 186.22Ah = 0.9% delta
so less than 1% degradation and even if that is true that is an excellent number as that will mean a battery life of 20+ years to get to 20% degradation from original capacity.

Now on last photo you can see how much was the battery used and what my house used.
So over 8544h (that is about 356 days) the house used a total of 1122.349kWh + 373.944kWh = 1496.293kWh that is an average of 4.2kWh/day or 126kWh/month
Out of all that 806.714kWh went trough battery so in average day 2.27kWh went out of the battery and that is about 47% of the battery capacity that is around 4.8kWh
There are of course multiple small cycles each day but it will be equivalent with 356 cycles at 47% DOD (very rough approximation). The idea is that using the battery this way makes no impact on battery degradation and all the degradation is related to battery calendar aging degradation (small chemical reactions inside the battery).
The largest impact by far on battery calendar degradation is battery temperature and as an approximation each 10C higher temperature doubles the rate of degradation.
My battery is always at a nice +18C to +22C for about half the year (winter) and the other half is at +22C to +26C so ideal temperature.

So battery temperature (that for this LiFePO4 is basically the same as ambient as they do not generate almost any self heat in typical offgid usage) is the most important factor in battery life and cycle is completely irrelevant for this type of cells.

There is quite a bit of detail in here so that in a year time I can do this test almost the same in order to remove as many variable as possible.

soc99.jpg

soc89.jpg

soc80.jpg

soc80-2.jpg

soc70.jpg

soc60.jpg

soc50.jpg

soc39.jpg

soc30.jpg

soc20.jpg

soc10.jpg

soc1.jpg

soc0.jpg

energy.jpg

graph.jpg

about1.jpg






Dacian Todea

unread,
Jul 16, 2020, 7:36:31 PM7/16/20
to electr...@googlegroups.com
There are almost 3 years since initial battery install and capacity test it just happened that I wake up earlier today and decided to do a battery capacity test as it was clear sky and sunny.

16.07.2020
I have not spent to much in to charging the battery as in the test made in 2018 as I did not wanted to wait another hour or so to slowly charge and top balance the battery so maybe there was some half an Ah more that could have fit in the battery tho sure not much more.
While this is still a good result it is not as great as the one done after one year. Do not even know the exact results I I need to make the computation below as I write this.

The same equipment was used (same current shunt with same calibration) but even so there are variations in the test and difference are small enough even after 3 year that there is some margin of error.

There are 25462h since the battery was installed as you can see on the SBMS120 About screen that translates to 1061 days so not quite 3 years but close enough.
The house (excluding heating) has used a total of 2664.519kWh + 2610.598kWh = 5275.117kWh an average of 4.97KWh a slight increase over the first year.
Form that trough battery are 2968.104kWh 2.8kWh/day again not an insignificant increase over the first year and as battery now is around 4.66kWh so an average of 60% DOD every day significantly higher than the 47% in the first year.

The battery capacity is 179.63Ah or 4660.7Wh that is when all cell where around 3V see photo with 0% SOC the one where cell 4 was 3.004V the capacity photo was just seconds after so to be the same I did in earlier test years ago.  I also left the lowest cell go to 2.8V and it did not took much to get there the capacity there was 180.47Ah but I will not use this number for comparison is just good to have for test's in the future.

So if I were to compare with the original capacity I have this
2017     187.89Ah    4.895kWh
2020     179.63Ah    4.660kWh
_______________________
3y          4.4%            4.8%

So degradation after 3 years is 4.4Ah if I consider the Ah counter and even larger 4.8% if I consider the Wh energy counter.
That is 1.5 to 1.6% degradation per year where I assume the calendar aging degradation is about 1% per year (fairly similar to what spec mentions at ambient around +25C) and the rest of 0.5 to 0.6% is form cycling.
I guess I may do the next test in 2022 when battery will be 5 years old.

Below a few photos not as many as in 2018 as I could not pay that much attention to the battery SOC. It was not as excited as the test in 2018 :)

charge.JPG

chargegraph.JPG


soc99.JPG

soc95.JPG

soc75.JPG

soc45.JPG

soc35.JPG

soc30.JPG

soc19.JPG

soc10.JPG

soc1.JPG

soc0.JPG

discharge-cap1.JPG

soc0-2.JPG

discharge-cap2.JPG

about.JPG





     
 