MG,
Check your ADC1n shunt sense wire connection both on the shunt side and on the SBMS0 side as it is open circuit and that is why you see that -600A (that is when that wire is not making contact open circuit).
Then when you fix that go to ADC menu and set you current shunts correct resistance value as that is the reason your current value was always wrong.
For the battery shunt you say you have a 150A 75mV shunt so Resistance will be 75mv/150A = 0.5000mOhm so that is what you will set in the ADC menu then for PV shunt you will set 75mV/75A = 1.0000mOhm
After you are doing this go to Device settings ans push the Save device settings so this are permanently stored so even if you do a power cycle the current shunt settings will remain saved.
As for the video. What you see there is voltage drop on sense wires while cell balancing is active. Those voltage drops seems a bit high so please check you sense wires connections. Make sure all 12 cell sense wires are connected as it may look like you did not connected all 12 wires or some are not making good contact. In any case during cell balancing there will be some voltage drop just slightly less than what you see in that video.
Nothing is wrong with the SBMS0 you just need to check your connections as you have some bad connections and also make the correct settings.