Hi Dacian,
I have a 24 V / 560 Ah LiFePO4 house battery on a cruising boat, consisting of 16 × 3.2 V / 280 Ah prismatic cells in a 2P8S configuration, controlled by an SBMS0.
I am currently improving the fire/thermal safety of the battery installation. The battery will be surrounded by non-combustible thermal/fire barriers, with approximately 50–100 mm free space above the cell terminals and a controlled ventilation path from this upper space to outside the living area.
I am considering installing the recommended 10 kΩ B3950 NTC connected to XT1 in the upper gas collection area or at the entrance to the ventilation duct, rather than attaching it directly to a cell.
The purpose would be to detect an abnormal temperature rise or hot gas release from a cell and have the SBMS0 immediately disable both charging and discharging through the EXTIO controls.
I have a few questions:
The objective is not to use XT1 as the primary protection against thermal runaway, but as an additional early shutdown layer: if abnormal heat or hot gases reach the enclosure exhaust area, all charging sources and loads should be switched off before the situation develops further.
Thanks,
Helles
Subject: SBMS0 Type 5 – Blue Sea 7702 vs. 7717 battery disconnect
Hi Dacian,
I would like to follow up on your recommendation to use Type 5 to isolate the battery and keep it isolated until the tripped circuit is manually reset.
I am considering two 24 V Blue Sea ML-RBS battery switches for the main battery disconnect:
Blue Sea 7702 – bistable
- Requires a momentary pulse to switch OPEN or CLOSED.
- After the pulse is removed, it remains in the selected state.
- Therefore, after a Type 5 trip opens it, it could remain OPEN even if the Type 5 output later resets automatically. A separate deliberate CLOSE command would be required.
Blue Sea 7717 – Auto-Release
- Requires a continuous control signal to remain CLOSED.
- Loss of the control signal causes it to OPEN.
- My concern is that if Type 5 resets automatically after the fault condition disappears, the control signal might return and the 7717 could close again automatically.
Which of these two switching behaviours would you recommend for use with SBMS0 Type 5?
Would the 7702 bistable/pulse-operated version be the better match for the manual-reset safety behaviour you described, or would you recommend the 7717 Auto-Release with some additional latching/reset circuitry?
Also, can the Type 5 output directly provide the required control signal, or should it operate the Blue Sea switch through an interface relay?
Thanks,
Hellmut
BMS signal is active +24V on the Orange wire.
The 7702 sits CLOSED.
BMS output drops from +24V to 0V.
The voltage transition on the Orange wire triggers the internal latch inside the 7702, snapping it OPEN.
Power to your system is cut instantly.
Fault clears; BMS output goes back from 0V to +24V.
The 7702 remains OPEN. The Blue Sea 7702 only responds to rising edge signals on its Brown wire to close. A rising voltage on the Orange wire is ignored for closing operations.
The system stays safe and disconnected indefinitely regardless of what the BMS is doing.
An operator walks up to the control panel and presses a physical NO (Normally Open) Momentary Pushbutton.
The button feeds a momentary +24V pulse to the Brown wire.
The 7702 snaps CLOSED and restores power.
Signal Input: The control input pins on the Blue Sea 7702 pull less than 10 mA continuous sensing current when state changes.
BMS Output Limit: Since your BMS provides max 50mA, it will trigger the 7702 switch input reliably without overloading or frying the BMS output stage.