Hi All,
Because of problems with our earlier 8 RJ house bank prismatic cells we are expanding our house bank on our catamaran from 540 to 840 ahrs rated, using new 12 EVE LF280K cells from Docan Power. These cells are all from the same batch. They have been closely tested and matched at Docan Power with capacities at 308-310 ahrs each, internal resistances at .15-.16mohm and are resting at 3.261-3.263 vpc. Those figures are exceptionally close and much closer than my earlier RJ cells.
We currently plan to assemble the 12 cells into one compressed bank of 4 series sets of 3 parallel cells each (4S3P) for a 12 volt nominal bank, one Electrodacus SBMS0 BMS and an external NEEY active balancer to help with balancing. We need these cells to remain in service for at least 10 years and as closely balanced as possible. Charging is primarily from two nearly equal sets of 24v nominal solar panels, total 1560 watts with two Victron 50 amp MPPT controllers.
Here are a couple of questions to confirm my thinking before assembling this pack:
· Given the matching and testing that has already been done, and very tight capacities and internal resistances, is there a need to recheck the capacities and top balance the cells before we put them in service? We do have equipment to do that, but I have concerns about unnecessarily stressing these already well matched cells.
· Other than using a 10 amp active balancer with single balance wires on each of the 4 sets is there some other way to ensure that the parallel cells within the sets remain in balance?
· Should I give any consideration to arranging the 12 cells in 3 separate batteries with 3 BMSs and active balancers? With BMSs like the SBMS0 I don’t see how that could work at HVD/LVD without the danger of suddenly disconnecting the separate batteries from the charging and load busses. Using direct control or smaller external relays to disconnect the charging or load sources from multiple batteries if a cell fails seems like an unworkable plan to me. I guess that can work with internal Mosfet BMSs disconnecting individual batteries but not external relay BMSs like the SBMS0. Also, there are Dacian’s concerns about multiple batteries in parallel and the significant expense of extra equipment required.
Thanks in advance for your thoughts and advice. Dave SV Soggy Paws
Many thanks to all that responded to my post with questions regarding testing 12 new EVE LF280K cells from Docan Power and how to best to configure the new LFP house battery pack.
From the responses it’s clear that not all agree on how best to do this. But having learned quite a bit from our first effort 4 years ago, we have reached some conclusions. We now believe that our original cells’ failure was due to several possible factors including original cell quality issues, connection and wiring resistance problems, significant balance variances that our small passive balancer was unable to resolve, and our own inability to recognize and address these things while underway much of last year.
So we have spent quite a bit of time recently researching these issues. From that effort it is a bit clearer now than it was then that some equipment and build methods will work better for us than others. And your responses have helped to confirm what we now think is best for us. As overseas cruisers in a marine environment our situation is different from others like off grid and RV builds.
Regarding testing, we plan to take all the new cells to a top balance of 3.55vpc which we think is a reasonable voltage to represent 100% SOC without stressing the cells. Since there is very little additional capacity above that, we see little reason to go higher and this ensures all cells start life in balance. Additionally we plan to only capacity test a sampling of 3 of our 12 cells between 3.55vpc and 2.8vpc. This is what several experts recommend and where the defaults are set by Dacian at Electrodacus for HVD and LVD. This will give us a good idea of the accuracy of the factory testing and our equipment. We plan to use our excellent ZKETECH power supply and load tester for this work.
Regarding configuration, we plan to go with a 3P4S arrangement that puts 3 cells in parallel and 4 of those sets in series. All cells will reside in one custom fiberglass box with compression and be monitored and controlled with one Electrodacus SBMS0. We will use our excellent NEEY 10a Smart active balancer which, unlike most others, has fully adjustable parameters to ensure the sets remain well balanced. The key to this arrangement is to ensure we start with well-matched cells. And we need to be very careful with assembly of the wiring and cell connections so that resistance is kept to a minimum and the parallel cells can easily remain in balance. This number of cells would allow us to reconfigure to 2P4S or even 1S fairly quickly in the very remote chance that there was some developing problem with a cell in the future.
We think that there are just too many issues and not enough reason to compel us to make the changeover to parallel batteries now. For us these issues include the added expense and complexity of reconfiguring to multiple batteries and internal Mosfet BMSs in order to protect our equipment in case of a HVD/LVD event. Also, we don’t see the rational for multiple batteries as backup when we can easily reconfigure a multiple cell single battery if needed. And then we also have the capability to switch to a start battery if we have a temporary emergency. Evidence shows that well matched, quality grade A cells that are well cared for just don’t degrade suddenly, especially after the first few months of use. And as is mentioned elsewhere, there is no way parallel cells will get significantly out of balance as can multiple batteries, unless there is an internal short, which will quickly be visible even on the series cells monitoring.
Finally, since we already have high quality external relay BMSs and other equipment for a complete system with backups, there is no compelling reason we can see to make these changes.
Again, thanks for all your advice. Dave and Sherry, SV Soggy Paws, Still In SE Asia