Casey,
Each DSSR20 requires around 2mA as control and so each EXT IOx can handle about 15 DSSR20
Also 30x DSSR20 will result in about 600 to 660A of charge current continues depending on panels and can peak around 750A the max of what SBMS0 can measure anyway.
With dual PV array setup where not all panels are connected at the same time up to 48x DSSR20 can be used 32 + 16
The 750A limit is related to the way software is designed and the compression method used with base 91
Humans work in base 10 so if you set a limit of 3 digit for your value then you can display max 999 (10x10x10=1000)
In Hex base 16 with say two characters "FF" you can display max 255 (16x16=256)
In base 91 that I use and my limit of 3 characters I can store a value no larger than (91x91x91 = 753571) thus I limited the max current to 750.000A with mA resolution.
There are methods to increase this keeping the 3 characters limits but for now I think 750A is sufficient.