Just made an update about progress and some other details here
http://electrodacus.com/solarforum.html?place=msg%2Felectrodacus%2F3BRwaLva3qQ%2FGv0zqrRbBwAJ
Here I just want to talk about SBMS0 and DSSR20 diversion options.
The simple option is to have a set of two DSSR20 both connected to the same max 2x 60 or 72 cell PV panels say 2x 300W total 600W of PV
Then one of the DSSR20 will connect to battery and the other to a resistive heating element matching the PV array in this example say panels are 33V max power point 9A then both in parallel will be 33V 18A and so you will have a heating element of 1.833Ohms (33V/18A).
This DSSR20 will be controlled by the same EXT IOx but the DSSR20 connected to the heating element will have the logic reversed by a transistor and a optoisolator or some similar circuit so that when battery charging is not needed (battery is full) the heating element will be ON.
The disadvantage of direct restive element is that at best this is 80% efficient (a full sunny day) and worst day may be less than 20% but in average it will be around maybe 60% depending on the type of weather you have and while not great it may be good enough for simple applications where you do not need all the available energy anyway and you only heat some water not full house heating.
Now inside this are 4 individual diodes and I can use just the + and - terminals to have access to two groups of two diodes in series so energy dissipation will be equal in all diodes.
I measured the voltage drop on one of this connected on a small aluminum plate and this are the results
0.1A - 1.25V
0.5A - 1.40V
1A - 1.47V
2A - 1.52V
5A - 1.56V
10A - 1.60V and slightly dropping as it got hotter.
20A - 1.65V (probably not measured due to my constant current limited supply that can provide 12A max).
So you can see that no matther the current voltage drop is fairly consistent around 1.5 to 1.6V for the two series connected diodes.
Now you will want around 20 of this connected in series for 60 cell panels as that will give you the 30 to 32V max power point voltage in winter with cold panels can drop to 18 in series if heat is needed in summer also.
The bridge rectifiers seems to be the best value as is just $10 for 20 of this and they can do 600 to 700W to support two parallel panels.
Now each of this bridge rectifiers will drop 30 to 35W and that requires good cooling likely water cooling as that way you can interface that directly with your thermal storage if that is water.
I talked about this a few years ago so it is not a new idea but then I decided for my use to have the DMPPT450 build and used.
But this thing using diodes is a good solution for the SBMS0 so that SBMS0 + DSSR20's can now have all the functionality of the DMPPT450 even if slightly differently implemented and if you read the update (first link here) you will read also about the 18kW max PV array supported by the SBMS0 and how a larger array can be used for battery charging same way as DMPPT450 even if it will be just 3 power levels.
To make sure the idea is understood I will provide an example.
PV panels are constant current sources so they will provide current directly proportional with the amount of light and say there are 3 conditions with sunny 18A provided by the two 300W 60 cell panels then 10A and 1A (cloudy).
at 18A from PV:
With diode's 1.65V x 20 diode bridges in series 33V x 18A = 594W heat from 594W available so 100% efficient
With resistive heating 18A x 1.833Ohm = 33V and so 33V x 18A = 594W heat so same 100% efficient.
at 10A from PV:
With diode's 1.6V x 20 diode bridge in series 32V x 10A = 320W heat from about max that so again around 100% efficient
With resistive heating 10A x 1.833Ohm = 18.33V so 18.33V x 10A = 183W about 57% efficient only.
at 1A from PV
With diode's 1.47V x 20 diode bridge in series 29.4V x 1A = 29.4W of heat so again around 100% efficient.
With resistive heating 1A x 1.833Ohm = 1.83V so 1.83V x 1A = 1.83W of heat just around 6% efficient thus almost nothing.