What is the overvoltage recovery set at ?
For the charger to be allowed to start again highest cell voltage needs to drop below that over-voltage recovery limit say 3.4V
If it only takes 30 seconds or less for that to happen it means that maybe charge rate is to high for your battery but 40A charge for a 200Ah should be fine. It may also be possible that connections between cells are not that great so high contact resistance.
You can decrease that over-voltage recovery a bit maybe to 3.35V but I will first check that connections between cells are good. You can check the voltage drop on the connection while under a known load or known charge current (multi-meter set on mV) then you can calculate the contact resistance.
It may also be that cells are fairly low temperature as internal resistance increases quite a bit with lower temperature.
It will typically take minutes between charge stopping and re-enabling not seconds.