I moved the sense wire to the middle of the long cable between 3+ and 4-. I ran some additional test to try to identify the source of the problem before I replace the SBMS0 with the SBMS0 Ver 3 that I have on order. I plan on making several simplification wiring changes when I install SBMS0 Ver 3 so the problem may be rectified without identification.
Changes include
replacement of part of the 4 Channel Optical Coupler with EXIO5 and EXI06,
improve battery terminal connection by replacing aluminum pieces with stainless
steel Belleville springs, and relocating the SBMS0 to significantly shorten the
sensing wires to the maximum length provided.
My existing sensing wires are about 4 Meters long.
Just so it is
not a question, I rebooted the SBMS to make sure all parameter and advanced
parameter settings were factory except I corrected the external temperature
settings.
Test 1: No sun
yesterday so I used a Renogy DC to DC charger set at 30 Amps to charge. Charged from 50% SOC (just rebooted the
SBMS0) to about 58% SOC. At around 3.43
volts (displayed on Monitoring Screen 1, the screen changed and displayed the
screen titled “Press Keys to unlock”. The
Keys did not work. For ease of
reference, I will call this the “Keys screen”.
Once in a while, the Keys Screen would turn off and the Monitoring
Screen would turn on and then back to the Keys Screen. Initially, this happened frequently and
slowly took more time on each screen.
When screen changes slowed down, I found that the Keys would start to
work on the Keys screen just before the Monitoring Screen turned on. After a while, the hotel lights turned off
indicating that I reach Overvoltage Lock.
I turned all charging off.
Test 2: Sun was
available today. Still at 58% SOC but figured
that I was close to the Overvoltage setting.
Charging with sun at about 15 Amps results were approximately the same
as yesterday except I never reached Overvoltage Lock and I eventually got to
99% SOC. When the Keys screen was on, I
noticed a counter in the upper left corner that I think is a counter for the
time a cell reached 3.55 V that counted from 1 to 3 or 4 seconds and the screen
would change to the Monitoring Screen for a little while indicating that the
cell dropped below 3.55 V before reaching 6 seconds. Most cells were at approximately 3.45 V when
the Monitoring Screen was on. Therefore,
only at a very low sun charge rate of 15 Amps, have I been able to get to the
Overvoltage setting of 3.55 V for 6 seconds without reaching Overvoltage Lock
setting of 3.75V.
I am not sure if any of this is normal or if not normal is it related to the installation I did a couple of years ago that has been working fine until now, or if I may have a bad cell. When I remove the aluminum pieces in the battery connections, I can monitor individual cell voltages for a period of time to see if I have a bad cell. Is there any other way to determine if there is a bad cell?