I decided yesterday afternoon to do a battery capacity test as I was testing the new app anyway and battery was already fully charged.
As some may not want to read the entire thing I will start with the results of the test
Total usable capacity is 12.56kWh (482.6Ah) a capacity loss of about 6% from the last test a bit over 2 years ago when battery capacity was 13.34kWh (512.9Ah)
During this 2 years around 2000kWh where output from the battery representing the equivalent of just 150 cycles 100% DOD so the cycle plaid basically no role and all this capacity loss is due to aging degradation.
Thus around 3% per year capacity degradation for this particular battery.
I will have hoped for 2% degradation per year but 3% is not outside of what could be expected. But this means in 10 years it will be at 70% of original capacity instead of 80% I was hoping for.
For me is not an issue as I do not need this capacity and will work fine even after 10 years and this is still the most economical battery at this time.
It could be that my cells where some stranger quality rejects as they where fairly far from the spec capacity when new but is the only sample I have access to and purchased this specifically to test as as much as 80% of you are getting this particular cells due to excellent value it provides.
Here is a screenshot when I started the test yesterday 18:25. I used a 900W or so air heater as a load same as last time.
I reset the E_user disconnected the PV and started the test

This is the screenshot from this morning at the end of the discharge test 8:45

There is about a 2% cell imbalance when at the bottom but that can be part due to delta in capacity between cells and slight imbalance at the top. But that was the same last time also as I did not manually balance the cells for perfect balance but they where just slightly maybe 0.5% more balanced than now after two years based on the old test results thus maybe capacity degradation is 5.5% instead of 6% still not quite the 4% I was hoping for.
The reason it showed 10% SOC when load was disconnected has to do with the fact that I optimistically set the battery capacity to 520Ah will need to set it to around 480Ah to get accurate SOC calculation.
Regarding the amount of energy used from battery
Seems to be around 2000kWh over the past two years so around 3kWh per day from battery as a lot of energy is used directly from PV 4727 - 882 = 3845kW / 740days = 5.2kWh/day from PV mostly cooking, and some heating this of course excludes the diversion heating that is way more.
So say battery is 13kWh then 2000kWh/13kWh = 154 equivalent cycles and that is nothing maybe 0.5% total degradation over 2 years due to cycling and most of the degradation is due to calendar aging (just normal non reversible chemical reactions happening in the cell).
Some more screenshots taken during the test
And now the charging
Cell voltage graph
SOC and internal temperature graph. Very accurate SOC calculation other than the fact that I have the battery set as 520Ah when it should be 480Ah then SOC at the end of discharge will have been 0% instead of 10%
In conclusion this is still the best value battery that you can buy for energy storage.