The 173Ah is sure not correct.
It seems that you set the current shunt to correct 0.1000mOhm (guessing that was set correctly from the beginning).
I also guess you reset the energy counter when you started the discharge test.
Based on photo with the 10A charge current it seems current shunt was set correctly and was measuring correctly at that point in time. Was the SBMS0 ever powered OFF while all this images where taken ?
Since all look OK based on photos and description I can only guess that you have a bad connection on the shunt sense wires ADC1n/ADC1p and at some point ADC1n got disconnected maybe for a few minutes but if you checked the graphs you should have seen that spike to 900A (tho your test lasted for a few days so you may not have noticed).
Since there are maybe around 70Ah extra that means ADC1n should have been disconnected for about 5 minutes (could be all at one or a few times adding up to around 5 minutes).
If the ADC1n is disconnected (either on shunt side or on the SBMS0 connector) the battery shunt measurement will show a 900A load (max what this shunt can measure) and in a bit less than 5 minutes that will add up to around 70Ah
Maybe when you lifted the SBMS0 to look at it (possibly a few times during the test) the wire did not made contact and the SBMS0 incorrectly seen 900A adding to the energy counter error.