Harry, thanks for your comments.
*I do the charge termination of the MPPT and the SBMS0 HVD opposite from you. See my earlier Update post. MPPTs control charge and turn it off at 14.0v charge termination. If needed SBMS0 can safely disconnect solar panels using Type 1 on DSSR 50s at 3.55vpc or .2v above MPPT charge termination. (We use the MPPT VE connections for our Node Red monitoring.) This makes more sense to me than the opposite and still lets SBMS0 shut down charging if HVD needed. Victron MPPT and other LFP chargers are purpose built to control charging so why not let them do their job and use the SBMS0 do its job when required? It helps to have well balanced cells so that one cell does not reach HVD before the MPPT can reach charge termination. Earlier with over 100mv delta in cell voltages near charge termination that was the case. Our other two chargers, alternators and shore charger work the same with chargers doing their job controlling charging and SBMS0 using SSRs controlling HVD if needed.
2 *"balance as close as we can" with the tools we have is our goal and especially if it negatively affects MPPT charge termination. With the NEEY balancer we have the tool to do it so why not?
3 *I don’t know enough about how resistance affects monitoring small MV voltages to comment on this. However I can see that there is a noticeable MV difference between what the SBMS0 and NEEY/multimeter read. So it is an interesting challenge for us to find out why as we have time. I’ll defer to your and Dacian’s comments on this as we investigate.
Dacian, thanks for your comments.
You said: “At the end of charge above 100mV delta is normal and basically impossible to be less.” I don’t understand this comment as my 4S3P bank is now showing less than 15mv at charge termination and without any balancing. With the NEEY balancing I can bring that down to less than 2mv. Maybe it is not even necessary to balance for quite a while with this well matched EVE LF280K bank. And yes after charging has ended and the voltage gets lower the cell delta hovers around 8mv for the rest of the day with only the load on the bank. I will add your SBMS0 balancer to the mix soon.
You said: “if you ignore SBMS0 and force charge above that then that 4th cell can get to 3.8V well above what will be normal for LiFePO4.” I am not ignoring the SBMS0, but rather just using it to execute a HVD only if necessary, not as a daily charge termination control. It is there to do its job as needed. At no time do we force the charge above 3.55vpc as this is our HVD. See details above in notes to Harry.
You said: “There is no fixed voltage you can set the MPPT that will work correctly.
14V is too high and the highest cell will be guaranteed to get to around 3.7 to 3.8V…”
14.0v is the most recommended voltage for LFP charge termination by others with, like you, years of LFP experience. It is working well for us and many others now, gives us very close to full use of the bank’s full useable capacity, and still allows for a HVD at .2v/.05vpc above that if required. And above that we have set a full charge buss disconnect using the SBMS0 at your default of 3.75vpc. With this setup I see no reason not to do it this way rather using the SBMS0 terminating the charge at 3.55vpc and the MPPT at something above that and closer to the HVD Lock voltage.
I have not extended the cell monitoring ribbon cable and there are no fuses in this cable wiring. However, the SBMS0 ribbon cable and NEEY/UNI-T multimeter are wired to different but similar cell bar points and using different sense wires. How would you explain the roughly 8mv difference between what the SBMS0 and NEEY/UNI-T multimeter are reading? Maybe it is just different wiring and connection resistance?
Thanks for the interesting discussion. Dave





Hi Dacian,
Maybe my earlier wording “when required or when needed” is a bit confusing regarding the SBMS0 being able to execute a High Voltage Disconnect as a backup for a rogue cell going too high early or MPPT problems. As described in detail in earlier posts on this thread, BOTH the Victron MPPTs and the SBMS0 are permanently installed and able to individually terminate charging.
We have our excellent Victron MPPTs set to execute a charging termination at 14.0v on a daily basis. This is a commonly recommended setting for MPPTs. Victron MPPTs are built for that purpose for ALL battery chemistries, including LFP, according to their literature. This includes a Lithium setting (which we don’t use) and an Expert mode (which we do use) for fully adjustable custom parameter settings. I agree that other MPPTs may not be suitable, especially if they have long nonadjustable absorb times for LA batteries.
In our setup if for some reason the MPPT does not stop the charge, or if a cell goes high early, the SBMS0 will execute a HVD at 3.55vpc thus acting as a backup to stop charging. This HVD, and the High Voltage Lock disconnect at 3.75vpc, disconnects the charge source and gives us two backups to the MPPT failing. Having this small voltage separation between these three charge termination set points, means that the balance must be fairly close. This arrangement is common practice across much of the LFP professional installation industry. It is especially important to have these backups in the marine world where the environment can cause more frequent equipment failures.
Regarding cell voltage balance, it is not difficult using today’s modern technology, to get the cell balance much closer than your 70mv at the top of the charge. I agree, that if primarily using the BMS to terminate the charge, that is not necessary. But if using the BMS as a backup to a MPPT, as in a marine installation is desired, the cell balance needs to be closer. Over the course of less than a week’s charging our new installation, our 10a NEEY active balancer was able to bring our cell balance from over 100vpc where we started, to less than 5vpc. And it has stayed there for the past week without further balancing. So it is possible.
I fail to see how this use of both a MPPT and backup external relay BMS is not a valid setup, especially if using your excellent SBMS0 with its default settings controlling external relays or charging equipment directly at HVD. In my view this is far superior to installing an internal Mosfet BMS, like Daly or JK that disconnects the battery if there is a cell problem. This arrangement necessitates using multiple batteries and multiple other protections for installed equipment. Multiple batteries means battery balance problems unless all resistances across the batteries, connections, and wiring are equal. And then there is the issue of quality control and customer support with Asian equipment.
Again thanks for the discussion. Dave
Hi Dacian,
I agree that if using the default HVD of 3.55vpc “the SBMS0 will almost always terminate the charging with very little chance that MPPT will be able to if MPPT is set at 14.0v”… I would add and if the cell delta is relatively high at 70+mv. Your real world example, and our earlier experience, of the MPPT set at 14.0v (equals 3.5vpc) and the SBMS0 default set at 3.55vpc is a perfect example of what will happen if the cell delta is relatively large. One cell will go high early and reach HVD before the MPPT has a chance to finish its charge algorithm. So the bank never gets fully charged to reach full usable capacity and the SOC suffers inaccuracy.
Relatively large deltas may be the norm for LFP batteries with only the SBMS0 balancer on, but not with quality EVE cells initially top balanced and actively balanced when needed with our NEEY. For the past two weeks now our cell delta has been less than 15mv according to the SBMS0, mostly without any balancing. The NEEY is not like earlier dumb Heltec and similar active balancers with no user control, adjustable presets and a wide cell delta required before it can be activated. Also the NEEY does not need to be on all the time. In the future I will only use it if there is a growing cell delta, and then only during the last few minutes of the charge. I have adjusted its presets to turn on at 3.42vpc and off at 3.1vpc and if the cell delta is greater than 5mv according to the NEEY, not the SBMS0.
You said: “The SBMS0 will not be able to keep LiFePO4 lower than 70mV at the end of charge; in fact it will likely be above that.” And: “To keep LiFePO4 at below 70mV when battery is close to fully charged will require that charge current is reduced way too much, around 300ma…” Now I understand why I was having so much trouble keeping my earlier RJ cells balanced with just the SBMS0 balancer. That is precisely why I have the NEEY now and can use both the MPPT and SBMS0 to control my charging. A couple of additional benefits to using Victron MPPTs are that I can adjust the amount of charge amps going to the bank, minimize shading effects by splitting up the array with multiple MPPTs, and monitor their performance on our Node Red display.
Based on the above information and because we want to have the Victron MPPTs control our charging with the SBMS0 as a backup, I will take your advice not to activate the SBMS0 balancer also. Unlike other dumb balancers, because the user can adjust the NEEY presets, it knows where it is in the charge cycle and the user can make it react accordingly. We are not concerned with the few additional amps that might be used up with NEEY for a few minutes at the top of the charge in order get the benefits of using the MPPTs as they are intended. For anyone interested, you can simply Google ‘NEEY Active Balancer’ or’ Off-Grid Garage’ to learn more. Modern technology strikes again.
Marine LFP and other equipment installations are all about backups, especially in remote locations with no Home Depots around. We view having the SBMS0 back up the Victron MPPT as an ideal situation. We also like that we can carry a relatively small SBMS0 BMS, various DSSR relays and other LFP system components as spares. And since we have designed and built our own LFP system theoretically we should have the skills and tools to make repairs. This is a much better situation than having to have some shore based electrician do our system for us with ‘drop in’ batteries, multiple Chinese internal Mosfet BMSs, and unknown fusing and connections, all without a schematic.