when we look into the cable datasheet :

" TECHNICAL DETAIL FOR HAVELLS 3.8/6.6 THREE CORES, AL/COPPER COND.,
XLPE INSULATED, ARMOURED CABLES "

We see the above in the contents,
we understand that 3.8/6.6KV mean 3.8 KV (UE) and 6.6 KV (E),
that again mean the same cable can be used when the system is
unearthed upto 3.8KV level only we have to use and is the system is
earthed we can use upto 6.6kv voltage level.

I want to understand, what is meant by earthed system and unearthed system.

thanks
Sreedhar
Havels catalogue.pdf

manish tiwari

unread,
Jul 19, 2012, 3:45:12 AM7/19/12
to sreedhar thokala, Electrical Engineer

Follow IEEE 141:1993 (Red Book)

 

 

 

Resistance-grounded systems employ an intentional resistance connection between the electric

system neutral and ground. This resistance appears in parallel with the system-to-ground

capacitive reactance, and this parallel circuit behaves more like a resistor than a capacitor.

Resistance-grounded systems can take the forms of

 

a) High-resistance grounded systems

b) Low-resistance grounded systems

 

Investigations recommend that high-resistance grounding should be restricted to 5 kV class

or lower systems with charging currents of about 5.5 A or less and should not be attempted on

15 kV systems (Walsh 1973 [B37]), unless proper ground relaying is employed. The reason

for not recommending high-resistance grounding of 15 kV systems is the assumption that the

fault will be left on the system for a period of time. Damage to equipment from continued

arcing at the higher voltage can occur. If the circuit is opened immediately, there is no

problem.

 

In a high-resistance connection (R <= Xco/3, where R is the intentional resistance between the

electric system neutral and ground, and Xco/3 is the total system-to-ground capacitive reactance),

the overvoltage-producing tendencies of a pure capacitively grounded system will be

sufficiently reduced. In a low-resistance grounded system, phase-to-ground potentials are rigidly

controlled, and sufÞcient phase-to-ground fault current is also available to operate

ground-fault relays selectively.Xco is difÞcult to determine in a high resistance grounded system

without testing (Bridger 1983 [B7]), thus 5 A to 10 A is recommended for the phase-to ground

fault current limitation.

 

The ohmic value of the resistance should be not greater than the total system-to-ground

capacitive reactance (Xco/3). The neutral resistor current should be at least equal to or greater

than the system total charging current. For details on obtaining and testing the value of the

total system charging current. (See Bridger 1983 [B7].)

 

High-resistance grounding provides the same advantages as ungrounded systems yet limits

the steady state and severe transient overvoltages associated with ungrounded systems. Continuous

operation can be maintained. Essentially, there is minimal phase-to-ground shock

hazard during a phase-to-ground fault since the neutral is not run with the phase conductors

and the neutral is shifted to a voltage approximately equal to the phase conductors. There is

no arc ßash hazard, as there is with a solidly grounded system, since the fault current is limited

to approximately 5 A.

 

Another beneÞt of high-resistance grounded systems is the limitation of ground fault current

to prevent damage to equipment. High value of ground faults on solidly grounded systems

can destroy the magnetic iron of the rotating machinery. Small winding faults on solidly

grounded systems may be readily repaired without replacing the magnetic iron. However, not

having to replace the lamination with equipment installed on high-resistance grounded systems,

when a phase-to-ground fault occurs, is a benefit.

 

High-resistance grounded systems should require immediate investigation and clearing of a

ground fault even though the ground-fault current is of a very low magnitude (usually less

than 10 A). This low magnitude of continuous fault current can deteriorate adjacent insulation

or other equipment. As long as a phase-to-ground fault does not escalate into an additional

phase-to-ground fault on a different phase, resulting in a phase-to-phase fault and operating

the protective device, the continuous operation can continue. It is essential to monitor and

alarm on the Þrst phase-to-ground fault. If the fault impedance is zero, solidly connected to

ground, the high-resistance system takes on the characteristics of a solidly grounded system

until the fault is located and repaired.

 

The key to locating a ground fault on a high-resistance grounded system is the ability to

injection a traceable ground signal to the faulted system. This fault-indicating system permits

fault location with the power system energized. An oversized, large opening, special clamp

on type ammeter is used. Some skill is required in Þnding the location of the fault. (See GET-

35548 [B35] for additional information.)

 

High-resistance grounding will limit to a moderate value the transient overvoltages created

by an inductive reactance connection from one phase to ground or from an intermittentcontact

phase-to-ground short circuit. It will not avoid the sustained 73% overvoltage on two

phases during the presence of a ground fault on the third phase. Nor will it have much effect

on a low-impedance overvoltage source, such as an interconnection with conductors of a

higher voltage system, a ground fault on the outer end of an extended winding transformer or

step-up autotransformer, or a ground fault at the transformer-capacitor junction connection of

a series capacitor welder.

 

Low-resistance grounding requires a grounding connection of a much lower resistance. It is

common to have 5 kV and 15 kV systems low-resistance grounded. The resistance value is

selected to provide a ground-fault current acceptable for relaying purposes. The generator

neutral resistor is usually limited for large generators to a minimum of 100 A and to a maximum

of 1.5 times the normal rated generator current (Johnson 1945 [B28]). Typical current

values used range from 400 A (to as low as 100 A) on modern systems using sensitive toroid

or core balance current transformer ground-sensor relaying and up to perhaps 2000 A in the

larger systems using residually connected ground overcurrent relays. In mobile electric

shovel application, much lower levels of ground-fault current (50 to 25 A) are dictated by the

acute shock-hazard considerations. One final consideration for resistance-grounded systems

is the necessity to apply overcurrent devices based upon their “single-pole” short-circuit

interrupting rating, which can be equal to or in some cases less than their “normal rating.”


Regards,

Manish

--
Regards,
Manish D Tiwari
Mumbai , India

manish tiwari

unread,
Jul 19, 2012, 3:47:14 AM7/19/12
to sreedhar thokala, Electrical Engineer
Dear All,

Apart from this my understanding abt UE & E system is as follows:-

In earthed system the start point / neutral point of the system is earthed, whereas in unearthed system the neutral of the system in not earthed.

 

In earthed system, when there is earth fault, the voltage of the faulty phase will become zero and the voltage between the healthy phases and ground will be the same Vph/√3 (3.8kv/√3 or 6.6kV/√3)

 

In case of unearthed system, the voltage between the healthy phases and ground will become phase to phase voltage i.e. Vph-ph (3.8kv or 6.6kV).

Hence the insulation level of the cables for unearthed system need to be higher.

 

Hence in you example 3.8kV is UE and 6.6kV is E. so you can use 3.8kV (UE) /6.6KV (E) cable only for unearthed system upto 3.8kV ……….. or for earthed system upto 6.6kV

Also note that if the system star point is grounded through resistance  or impedance, then also the system shall be considered as unearthed system.