I am struggling with a Citect SCADA read of some data. The system is using the "Modnet3" driver over TCP/IP to talk with a system (Modnet 3 as its TCP/IP with first register at 0 and 0 to 15 bits). I am reading the modbus data into variables which is working fine for the analogue values all defined as real in citect.
2. Create Variable tag with word and bit in word (For Modnet3 address start from 0 and have bit 0 - 15 that means in you need to read device that start address are 400001 you should assign in citect as 400000).
Citect SCADA logging can be configured using the Computer Setup Editor which is part of the Citect SCADA suite.This application modifies the citect.ini file located in the C:\ProgramData\Schneider Electric\Citect SCADA2018\Config\ directory.This file can be used to adjust logging and filtering data by priority, category, or severity.