IDEA has received a request from an IDEA member in the MIddle East who is looking for advice about how to locate identify and repair leaks in a chilled water and condenser water loop. The setting is direct buried pipe in a high ambient temperature region. Any advice would be appreciated.

Edward T. Borer Jr.

unread,
Jan 21, 2013, 3:27:56 PM1/21/13
to district-co...@googlegroups.com

Consider acoustic locating for direct buried water leaks.

 

Ted Borer, PE, CEM, LEED AP

Princeton University

Energy Plant Manager

MacMillan Building, Elm Drive

Princeton, NJ 08543-2158

Ph:(609) 258-3966

Fx:(609) 258-1508

Cell: (609) 731-2327

Home: (609) 466-3322

etb...@princeton.edu

 

Learn about our plant on YouTube: http://www.youtube.com/watch?v=xwHhbDvpdS4                                                                                                                                   

--
You received this message because you are subscribed to the Google Groups "District Cooling Forum" group.
To view this discussion on the web visit https://groups.google.com/d/msg/district-cooling-forum/-/hkptRocp8nEJ.
To post to this group, send email to district-co...@googlegroups.com.
To unsubscribe from this group, send email to district-cooling-...@googlegroups.com.
For more options, visit this group at http://groups.google.com/group/district-cooling-forum?hl=en.

Rundle, Gordon

unread,
Jan 21, 2013, 4:45:11 PM1/21/13
to district-co...@googlegroups.com

We have used various means to locate leaks in our chilled water distribution system including:

 

·         Visual – Sometimes just walking the route will result in some clues where to start. You may find some wet areas that are suspect.

·         Thermal Scanning – With the high ambient temperatures this may  be a good option. However,  if the leak is small and the lines are deep it may not show up in the scan.

·         Acoustic / Ultrasonic Scan – Personally,  I have had the best luck with this type of detection.  It is basically a technician listening with a microphone from ground level, or utilizing transmitters installed on the pipe. Accuracy will be affected by the interference of surrounding noise (i.e. traffic, plant equipment). So the quieter, the better.

·         Gas detection – Depending on the size (volume) of the lines, they can be filled with a gas such as helium. Holes are then drilled above the pipe , to approx, the depth of the pipe,  every 15’ or so along its path. Utilize a gas detector above the holes , the highest concentration of helium should indicate where the leak is. Accuracy will be affected by the porosity of the soil and back fill . If the pipes were bedded in stone, it will be difficult to detect as the gas will diffuse prior to rising from the hole. Likewise, if the pipes were jacketed in poly wrap, the gas will not have a direct path to the surface.

·         Dig and Sectionalize – If the above options do not work this may be the only option. Dig up the line in the center of the run, cut out a section, and hydro test both sides. From there, you should be able to determine which side has the leak. Repeat until leak is found.  We recently had a leak during construction. The contractor had installed approx. 1000’ of 20” pipe that was found to have a leak. After the acoustic scan (city streets to much noise) and gas detection  (poly-wrap on pipe) failed, we had to go this route. While labor intensive, we were able to locate the leak in about 3 days.

 

Regards,

 

Gordon Rundle

Engineering Project Manager

ct graphic

366 Kentucky Ave, Indianapolis IN 46225

Office / Fax 317.693.8854

 

 

 

From: district-co...@googlegroups.com [mailto:district-co...@googlegroups.com] On Behalf Of Len-IDEA
Sent: Monday, January 21, 2013 3:23 PM
To: district-co...@googlegroups.com
Subject: {District Cooling Forum} Leak in chilled water/condenser water loop in MIddle East

 

IDEA has received a request from an IDEA member in the MIddle East who is looking for advice about how to locate identify and repair leaks in a chilled water and condenser water loop. The setting is direct buried pipe in a high ambient temperature region. Any advice would be appreciated.

--

Reply all
Reply to author
Forward
0 new messages