"Loop" in chilled water distribution piping system

40 views
Skip to first unread message

Stephen

unread,
May 29, 2015, 12:24:16 PM5/29/15
to district-co...@googlegroups.com
We are designing a new district cooling plant and the question has come up regarding the benefits of "looping" the chilled water distribution piping.  We have included a loop in some of our district cooling plants and in others we have not.  I'm curious if anyone has evaluated the benefits of looping the chilled water distribution.  The primary benefit we have identified is the ability to utilize valves to isolate various sections of the pipe and thus contain the impact of a potential pipe break/leak.  It would seem there are other hydronic benefits, but I have not found any research to support the benefits.

Has anyone else faced this decision?  Thanks for your feedback!

Stephen Koontz

Edward T. Borer Jr.

unread,
May 29, 2015, 12:50:23 PM5/29/15
to district-co...@googlegroups.com

Our system includes a few loops.

It seems to make troubleshooting a bit harder, but hydraulics will be a little more energy efficient. It can be a long time between someone accidentally closing a valve and the problem being discovered.

The more valves and loops you add, the more instrumentation should be included.

 

Ted Borer, PE, CEM, LEED AP

Princeton University

Energy Plant Manager

MacMillan Building, Elm Drive

Princeton, NJ 08543-2158

Ph:(609) 258-3966

Fx:(609) 258-1508

Cell: (609) 731-2327

Home: (609) 466-3322

etb...@princeton.edu

 

Princeton Energy Plant during Hurricane Sandy:  http://youtu.be/WtjIj91imSQ

 

“It would go a long way to caution and direct people in their use of the world, that they were better studied and knowing in the Creation of it. For how could [they] find the confidence to abuse it, while they should see the great Creator stare them in the face, in all and every part of it” William Penn, 1693

--
You received this message because you are subscribed to the Google Groups "District Cooling Forum" group.
To unsubscribe from this group and stop receiving emails from it, send an email to district-cooling-...@googlegroups.com.
To post to this group, send email to district-co...@googlegroups.com.
Visit this group at http://groups.google.com/group/district-cooling-forum.
For more options, visit https://groups.google.com/d/optout.

Coolsol...@aol.com

unread,
May 29, 2015, 12:50:33 PM5/29/15
to district-co...@googlegroups.com, smko...@trane.com
Stephen,
 
A CHW "loop" has advantages over a traditional "spine and branches" layout (although the loop will often have a higher first cost).  As you noted, the loop provides the flexibility to isolate areas of the network, without cutting off access to other users.  In addition, the loop can often avoid bottlenecks in piping capacity and/or allow larger loads to be served with smaller bore piping.  Of course, a detailed hydraulic analysis will quantify the differences.  Locating satellite CHW plants and/or remote Thermal Energy Storage (TES) along the network can also have a positive impact on addressing all the above issues, whether the network is a loop or a spine.
 
John S. Andrepont, President
The Cool Solutions Company
5007 Lincoln Avenue, Suite 201
Lisle, IL 60532

Issa Qandeel

unread,
Jun 1, 2015, 7:47:46 AM6/1/15
to district-co...@googlegroups.com, smko...@trane.com

Stephen,

Other than the benefits of isolation (which is real important when failures start occurring with time), the one important benefit is the flexibility the looping provides to add unplanned developments to the network in the future. With adequate isolation measures you can always tap into the existing network (using the isolation valves) rather than having to go through hot-tapping or freezing.

 