Dear John,

 

Thanks for your input. Much appreciated.

 

The design that I am working on is a chilled water storage plant not stratified tanks.

 

I have noticed from past experience that there is always been an element of mixing in stratified installations.

 

My new design has been concentrated on, no mixing of chilled water and no glycol as our design temperature is 38.3 F.

 

I have designed the rolling tank method which completely eliminates any form of mixing of chilled water. This coupled with low temperature water offers enormous benefits to the Thermal storage plant installation.

 

In  actual fact, I was able to design this plant plant at almost the cost of a conventional plant. Thermal storage plants using ice plants, as you may well be aware is approximately 1.4 to 1.6% more expensive than conventional systems.

 

The design being such, has resulted in there not being a motivation for payback periods as the plant starts to save money immediately.

 

In South Africa, there is no installations using low temperature 38.3F supplied to AHU’s.  The conventional 42.8 F has always been used.

 

We have used lower temperature water on the primary circuit but this has always been mixed/ combined with plate heat exchanger- with the return water to supply 42.8F to the building.

 

Please let me know if you have done similar installations.

 

 

 

Rickey Naidoo

Pr Tech (Eng) M Tech ( Eng) GCC fact. MASHRAE

 

 

Naidoo & Associates

Consulting Mechanical Engineers

30 Tamarind Cl

Somerset Park

Umhlanga

Tel/ Fax 0315621706

cell 0829591278

Non-performers focus on obstacles. Performers focus on results.

~Nido Qubein

 

 

 

 

 

 

 

 

 

 

 

From: Coolsol...@aol.com [mailto:Coolsol...@aol.com]
Sent: Monday, September 15, 2014 9:31 PM
To: jho...@stny.rr.com; district-co...@googlegroups.com
Cc: ric...@telkomsa.net
Subject: Re: {District Cooling Forum} Very low-temperature district cooling system des...

 

Dear Rickey,

 

Like you, I too am a consulting mechanical engineer; my business focuses on consulting related to TES, District Cooling, and Turbine Inlet Cooling.  I concur with your Low Temp Water TES concept and the benefits you mention relative to non-TES systems and to Ice TES and Water-Glycol TES systems.

 

I am assuming that the concept uses water TES which is thermally stratified (less dense CHWR over more dense CHWS) in a single insulated TES tank, as has become quite standard for several decades now.  The minimum CHWS temperature limit for thermal stratification of plain (pure) water is theoretically 39.4 degF (4.1 degC), which is the temperature at which maximum density occurs for pure water.  It is common to have some impurities dissolved in the water (a few hundred ppm) as well as some water treatment chemicals for corrosion inhibition and microbio control (perhaps several hundred to one thousand ppm).  Thus it is possible to stratify the water at temperatures very slightly below the 39.4 degF minimum for pure water.  Your suggested supply temp of 38.3 degF may be slightly lower than you can actually achieve with nominally pure water.

 

There have been a number of stratified Low Temp Fluid (LTF) TES installations installed, operating at CHWS temps well below the pure water minimum.  Some have a supply temp as warm as 36 degF, while others are as low as 30 degF or less.  In each case, they use an aqueous fluid with dissolved corrosion-inhibiting salts, in a concentration (from 3 to 7 weight %) chosen to suit the desired supply temperature.  This LTF TES system is patented and uses the trade name SoCool.  This LTF compares very well with water-glycols, as the LTF is relatively low cost, has thermophysical properties quite close to those of plain water, and also eliminates the need for on-going water treatment for corrosion and microbio control.

 

Accordingly, your suggested Low Temp Water TES approach for DC makes good sense, but may be limited to minimum supply temps of ~39 degF.  For much colder supply temps, SoCool TES can be, and has been, used.

 

Please contact me anytime, if you have further TES-related questions.

 

John

 

John S. Andrepont, President

The Cool Solutions Company

5007 Lincoln Avenue, Suite 201

Lisle, Illinois 60532 U.S.A.

 

In a message dated 9/15/2014 1:14:24 P.M. Central Daylight Time, jho...@stny.rr.com writes:

Len,

 

The best person for this request would be John Andrepont.

Joseph C. Hoose


On Sep 15, 2014, at 2:07 PM, Len-IDEA <len....@gmail.com> wrote:

Posted on behalf of Rickey Naidoo, a consulting mechanical engineer in South Africa seeking comments from IDEA on his very low temperature non-glycol, non-ice district cooling design using water for TES; your reply will automatically be emailed to him.

I am South African consulting engineer located in South Africa and have designed a thermal storage plant using supply chilled water temperature of 38.3 F returning at 53.6 F (12F). I am interested to know if there are any similar applications using 38.3F chilled water in the US and would be interested to know of the challenges that has been experienced using colder water.

I have opted to make chilled water as I wanted to stay away from Glycol and ice plants.Trane makes a chiller can safely make chilled water at 38.3 F.

The net effect of this design promises the following benefits:

  • The chillers ( the source of making the chilled water) reduced in capacity by almost 50%
  • Due to the type of chiller used, the water could be stored down to 3.5C without the use of Glycol. ( Glycol is used to lower the freezing point of water to protect the chillers and is very costly in storage applications). Chilled water is normally used at 6C in chilled water applications.
  • The chilled water storage capacity was reduced by almost 40%
  • There was a huge reduction in the cost of the air conditioning installation as there was no major storage capital equipment used. The only major cost was the cost of the thermal storage tanks.
  • The chilled water pipe sizes to the building was reduced due to the reduced water supply temperature. (In at 3.5C; out 12C). This offered substantial savings to the project. Reduced air-handling unit sizes due to the larger temperature difference across the cooling coils
  • Reduced pump sizes due to the 30% lesser water being pumped to the building.
  • No payback motivation required as the cost of the thermal storage plant was equal or cheaper than a conventional chilled water air conditioning system. Conventional air conditioning systems does not use storage. The chilled is sized on the full size chillers required to satisfy the air conditioning to the building.
  • Huge electrical savings as the plant does not work on maximum demand periods using the local 2 part electrical tariff. The client only pays for reduced cost energy charges, which are billed at a cheaper rate at night.
  • 42% cheaper energy consumption when compared to a glycol chiller making ice on a Calmac installation. Glycol chiller COP is 3.9 whilst the chiller making chilled water at 3.5C operates at a COP of 5.6 during the night charge of the chiller.
  • Lower maintenance system as no Glycol is used on the system. Glycol installations are very corrosive to the valves and fittings.
  • Unlimited lifespan as the chilled water tanks can last for a very long time.
  • Simple controls for the mechanical installation.

--
You received this message because you are subscribed to the Google Groups "District Cooling Forum" group.
To unsubscribe from this group and stop receiving emails from it, send an email to district-cooling-...@googlegroups.com.
To post to this group, send email to district-co...@googlegroups.com.
Visit this group at http://groups.google.com/group/district-cooling-forum.
For more options, visit https://groups.google.com/d/optout.

=

Coolsol...@aol.com

unread,
Sep 16, 2014, 11:27:59 AM9/16/14
to district-co...@googlegroups.com, ric...@telkomsa.net
Dear Rickey,
 
All the TES tanks we've been discussing (the SoCool LTF TES at Princeton U and DFW Airport, and elsewhere, as well as the many other CHW TES tanks) are thermally stratified TES tanks.  With proper diffuser design, the mixing is quite minimal.
 
I am not familiar with the term "rolling tanks method."  Is this similar to the "empty tank method" used ~25 to 30 years ago, in which multiple "N" tanks are used, where the water volume can be fully contained in "N-1" tanks, and where one tank begins empty, then receives water until it is full, then the newly empty tank becomes the receiver, etc. and both supply and return water are never in the same tank at the same time?  Or is the rolling tanks method something else?
 
John
 
John S. Andrepont
The Cool Solutions Company
 
In a message dated 9/16/2014 9:55:35 A.M. Central Daylight Time, spc...@burnsmcd.com writes:

Hi Rickey,

 

Yes, 36 F all the way to the coils and the design was original to the airport construction (very innovative for 1970). 

 

We did some coil control valve changes as part of a major renovation and a new terminal construction to achieve a >24 F design delta T using 1/3 and 2/3 coil flow split control.  In some cases we achieved 28 degrees, which blended with older terminal returns (which were less than 24) to average the 24 F delta we needed for the tank design.

 

Yes, it was a stratified water tank. 

 

SoCool depresses the maximum density/temperature relationship (below 39.1 F), such that mixing does not occur. 

 

We had a very tight stratification layer, approximately 1-2 feet (<3%) on a 60 foot tall tank.

 

Feel free to call me at (817) 840-1233, if you have further questions.

 

Best Regards,
Scott

 

From: Rickey Naidoo [mailto:ric...@telkomsa.net]
Sent: Tuesday, September 16, 2014 9:17 AM
To: Clark, Scott; district-co...@googlegroups.com
Subject: RE: {District Cooling Forum} Very low-temperature district cooling system design from South Africa using water for TES.

 

 

Great stuff,

 

I would be interested to know if 36 F water was supplied to the AHU’s and what precautions you have taken for the insulation.

 

Also, was this a stratified tank installation ?

 

The design that I am currently working on is chilled water thermal storage plant. I have had extensive experience with stratified tanks and have still found mixing on the installations.

 

I have designed the rolling tanks method, which completely eliminates mixing and combined this with low temperature water to achieve enormous savings on the thermal storage plant applications.

 

Many thanks for your input.

 

 

Rickey

 

 

From: Clark, Scott [mailto:spc...@burnsmcd.com]
Sent: Monday, September 15, 2014 9:53 PM
To: district-co...@googlegroups.com
Cc: ric...@telkomsa.net
Subject: RE: {District Cooling Forum} Very low-temperature district cooling system design from South Africa using water for TES.

 

We did a similar design at DFW Airport using 36 F degree supply, with SoCool, and a 60 degree F return.  The tank is 6 MG and 90,000 ton-hours.

 

It’s been in operation since 2004 with good success. 

 

There was a minimal de-rate to the chillers, but it was not significant.

 

Thanks,

 

Scott Clark, P.E., CEM

Practice Leader, OnSite Energy & Power

 

Burns & McDonnell

6500 West Freeway, Suite 700

Fort Worth, Texas  76116

817.840.1233 Office

817.233.1540 Mobile

www.burnsmcd.com

 

Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For

* Registered Engineer in Texas

This e-mail and any attachments are solely for the use of the addressed recipients and may contain privileged client communication or privileged work product. If you are not the intended recipient, and receive this communication, please contact the sender by phone at 817.840.1233 and delete and purge this e-mail from your e-mail system and destroy any other electronic or printed copies. Thank you for your cooperation.

 

 

 

From: district-co...@googlegroups.com [mailto:district-co...@googlegroups.com] On Behalf Of Edward T. Borer Jr.
Sent: Monday, September 15, 2014 1:16 PM
To: district-co...@googlegroups.com
Cc: ric...@telkomsa.net
Subject: RE: {District Cooling Forum} Very low-temperature district cooling system design from South Africa using water for TES.

 

Princeton (and many other plants) use water as cold as 31-degrees F. We use a 5.7% solution of nitrite/nitrate with a trade name of SoCool. That product allows us to store very cold water in a thermally stratified chilled water application. It won’t freeze until somewhere in the range of 25F. It results in a slightly different density and specific heat than water, so pumps and heat exchangers should be designed with this in mind. We do not operate colder than 31F so that un-treated water on the other side of a heat exchanger will not freeze.

 

Our thermal storage system is 2.6 million gallons. With a 20 degree differential temperature, that results in about 40,000 ton-hours of storage.

 

Glycol tends to be food for biological contamination. At the concentration we use, the nitrite/nitrate solution is an effective corrosion inhibitor and biological inhibitor. We have never had a problem with biological growth or corrosion since the system was installed in 2005.

 

Ted Borer, PE, CEM, LEED AP

Princeton University

Energy Plant Manager

MacMillan Building, Elm Drive

Princeton, NJ 08543-2158

Ph:(609) 258-3966

Fx:(609) 258-1508

Cell: (609) 731-2327

Home: (609) 466-3322

etb...@princeton.edu

 

Learn about our plant on YouTube: http://www.youtube.com/watch?v=xwHhbDvpdS4                                                                                                                                   

Rickey Naidoo

unread,
Sep 16, 2014, 11:57:31 AM9/16/14
to Coolsol...@aol.com, district-co...@googlegroups.com

I think the concept is similar but we only use 3 tanks -50% redundancy. I don’t know of any installations done previously.

 

Total volume of storage water is stored into 2 tanks with 1 tank empty.

 

Return water or generated chilled water fills the empty tank without any mixing.

 

Our chilled water storage is based on a rolling tank method. 

 

The design consists of 3 tanks. Each tank capable of holding 50% water.

 

At  night  tanks 2 and 3 are filled of  water.  ( common and hot tanks)

 

The charging Night  cycle works as follows :-

 

 

Water is drawn from common tank 2 and passes the the chiller to make 3.5 ⁰C water. Chilled water is accumulated  into cold tank 1 until tank 2 becomes empty.

Common tank 2 valve closes. Water is now drawn from Hot tank 3.

 

Water is then drawn from hot tank 3 and filled into cold tank 1. Tank 1 will overflow into tank 2. Plant will run until hot tank 3 is empty and common tank 2 is full.

 

 

Day cycle works as follows :-

 

You will have cold tank 1 and common tank full of cold water.

 

Cold Water is drawn from common tank 2 and passes the the airhandling units to cool the building. Hot water will empty into Hot tank 3 which is empty.

 

As common tank 2 becomes depleted, hot tank 3 becomes full.

 

Once common tank 2 becomes empty, tank valve 2 closes and tank valve 1 opens. Hot water from tank 3 will overflow into common tank 2.

 

 

Rickey

Coolsol...@aol.com

unread,
Sep 16, 2014, 12:23:36 PM9/16/14
to ric...@telkomsa.net, district-co...@googlegroups.com
Rickey,
 
Understood.  That is precisely the old "empty tank method."  There were many such installations in the US in the 1980s.  Some used as few as 2 tanks, some as many as ~15 tanks, most used ~4 to 6 tanks.  When using fewer tanks, there is a large premium capital cost as the "empty" volume is such a large % of the water volume.  When using many tanks, the extra % is small; but the cost per unit volume of smaller tanks goes up rapidly, also adding capital cost.  And for every tank that is used, there are required supply and return nozzles, valves, and piping, all sized for the full flow rate of the TES system; this adds a lot of capital cost too, especially for systems with many tanks.
 
Other issues were also apparent:
1) As each empty tanks is re-filled, the water is heavily aerated.  This often resulted in massive water treatment issues with microbiological growth.
2) Although cold and warm water are never together in any one tank at the same time, each tank must be repeatedly cooled and warmed as they are alternately filled with col and warm water.  This affected the supply water temp.
 
Once the thermally-stratified TES tanks became available in the early 1980s with turnkey supply including thermal performance guarantees, they became the standard in the market, replacing the earlier use of "one-off" designs such as:
A - the "empty tank method" TES,
B - TES tanks using flexible membranes to separate the two temperature zones,
C - TES tanks using rigid diaphragms to separate the two temperature zones,
D - "baffle-and-weir" TES tanks, and
E - "labyrinth" TES tanks.
 
John
 