John--Assuming the vertical tank is uninsulated, is it just acting like a heat exchanger dispensing heat into the manhole in order to condense the flash steam before it is injected into the condensate return?  If so, how do you know all the steam is condensing?  Couldn’t the high pressure from the trap discharge push all the water from the tank into the condensate return and then follow it with un-flashed steam?   

 

Wayne Kirsner, P.E.

kirsner consulting engineering, inc.

www.kirsner.org 770-953-8262


From: distribut...@googlegroups.com [mailto:distribut...@googlegroups.com]
Sent: Wednesday, March 12, 2014 12:16 PM
To: Abridged Recipients
Subject: {Distribution Forum} Abridged summary of distribut...@googlegroups.com - 4 Messages in 1 Topic

 

Group: http://groups.google.com/group/distribution-forum/topics

§                        District Steam Condensate Return - Flash Stream [4 Updates]

"Dageforde, Darren" <ddag...@unmc.edu> Mar 11 09:09PM  

At the University of Nebraska Medical center, we too try to take high pressure end of main drips to building mechanical rooms where we can hit a flash tank and safely vent it before we pump it back to ...more

Back to top

"MacKellar, George" <gdmac...@ftch.com> Mar 11 08:31AM -0400  

Hendrik,
 
There was an excellent discussion of this led by Wayne Kirsner at the recent Distribution Workshop in Atlanta. Wayne described a means to determine how much condensate from a high ...more

Back to top

"Edward T. Borer Jr." <etb...@Princeton.EDU> Mar 11 09:22PM  

Princeton tries to use flash tanks and hotwells in buildings for discharge from steam lines above 15 PSIG. Below 15 PSIG it is common to find trap discharge routed to the condensate line.
...more

Back to top

Rod Crichton <rcri...@londondistrictenergy.ca> Mar 12 12:46PM  

Hi Hendrik,
 
Here in London, we have a high pressure (190psi) steam customer approximately 3km away in which we pump the condensate back from. Located in steam vaults, the high pressure line traps ...more

Back to top

--
You received this message because you are subscribed to the Google Groups "Distribution Forum" group.
To unsubscribe from this group and stop receiving emails from it, send an email to distribution-fo...@googlegroups.com.
To post to this group, send email to distribut...@googlegroups.com.
Visit this group at http://groups.google.com/group/distribution-forum.
For more options, visit https://groups.google.com/d/optout.




This email is free from viruses and malware because avast! Antivirus protection is active.


Molnar, John

unread,
Mar 13, 2014, 1:12:01 PM3/13/14
to wayne kirsner, distribut...@googlegroups.com, Len Phillips

Wayne

The tank acts as a heat exchanger cooling the flash steam. If the traps are operating as design (even blowing through) the amount of discharge to the tank mixes with the already cooled condensate already in the tank and tempers the condensate temperature below the flash point. If a blowing trap generates more heat than the tank can cool through surface heat exchange and mixing with the volume of condensate in the tank the steam could the flash in the condensate main. Our traps discharge rate must not reach this point because we have not found this occurring in our system which is operating at 150 Lbs. @ 365 degrees. If this did occur the tank could be make bigger for larger exchange area and more tempering capacity. 

John

 

http://static.avast.com/emails/avast-mail-stamp.png

This email is free from viruses and malware because avast! Antivirus protection is active.

 

--

wayne kirsner

unread,
Mar 13, 2014, 10:40:15 PM3/13/14
to Molnar, John, distribut...@googlegroups.com, Len Phillips

John--I guess the tank would be full of liquid condensate.  My reasoning is that when the trap last cycled off (assuming it’s an on/off trap like a inverted bucket), the tank would be mostly full of flash steam.  As the flash steam condensed due to heat loss thru the vessel’s walls, it’s pressure would fall below that of the condensate return so condensate would push back into the tank and fill it (assuming no check valve between the tank and CR line).  When the trap next discharged, it would be putting flash steam into the condensate from above the condensate.  I agree this will not hammer, especially if condensate has not had time to subcool.

 

I guess the bottom line is—Does it work, meaning specifically, did it end waterhammer in the condensate return where you had it before

 

And, since the tank is effectively a condensate cooler, do you think it’s more cost effective than mounting a finned tube heat changer on the wall of the manhole and running the trap’s discharge thru it?

 

 

Wayne Kirsner, P.E.

kirsner consulting engineering, inc.

www.kirsner.org 770-953-8262

image002.gif

Molnar, John

unread,
Mar 14, 2014, 11:16:22 AM3/14/14
to wayne kirsner, distribut...@googlegroups.com, Len Phillips

Wayne

The bottom line answer yes it works very well. We have not found any signs of flashing steam in the tank or the return line.  They have eliminated  the corrosion leaks at the traps discharge connecting point on the return line. We have not had any of those leaks since we installed these tanks the last 5 – 7  years.  

John

Image removed by sender.

wayne kirsner

unread,
Mar 16, 2014, 6:43:26 PM3/16/14
to Len Phillips, distribut...@googlegroups.com

In the article I wrote for Chemical Engineering Magazine and the speech I gave at the Feb. 2014 Distribution Conference, THE POINT was—schemes to blend high pressure condensate into pumped condensate return lines DO NOT WORK to prevent waterhammer if:


Pumped condensate flow AND subcooling  in the PCR line are insufficient to continually condense all the flash from the high pressure trap discharge as it enters the PCR.  It does not matter whether your system uses a sparger to break up the flash steam bubbles or any other type of blender if the heat capacity of the condensate mass flow cannot condense all the steam as it enters the PCR.

 

  1. This means any heat extraction device from the high pressure condensate before it enters the PCR line (like a  tank or finned tube heat exchanger)  is going to reduce the flash steam and lesson or eliminate the surviving flash steam bubbles in the PCR.
  2. It also means that if there aren’t a lot of blowing HP steam traps directly into the PCR so that the temperature of the returning condensate stays low enough to condense all flash steam entering the PCR from HP traps, there will be no hammering.  This implies that a temperature and pressure gauge in the condensate return are important trouble shooting tools  ( the pressure gauge is important because it’s actually the subccoling of the condensate in the PCR that’s important to condensing the incoming flash steam from HP Traps)
  3. There’s a lot of money wasted on mixing or blending devices like a sparger or ejector that can help, but only in a limited way.  (Why they can help is  implied in the magazine article where I explain the marginal effect of incomplete mixing).

 

Waterhammer due to flash steam bubbles surviving in the PCR line is going to happen, if it happens, when one of these events triggers it:

  1. Another PCR branch with subcooled condensate joins the main PCR and has enough additional cool condensate to condense the surviving bubbles in the Main line. The waterhammer will occur at the junction of the lines in the Main.
  2. A large condensate pump cycles on that significantly increases the subcooled flow in the PCR so flash steam bubbles that formerly survived are suddenly condensed  in condensation induced waterhammers (this is what happened in the magazine article)
  3. A large steam trap cycles off changing the balance between condensate subcooling and entering flash steam, although I think this would be rare.

 

The magazine article features a busted check valve that did not survive a waterhammer even though flash steam from the high pressure trap it was associated with was delivered into the PCR thru a carefully designed sparger assembly.  

 

What I would like to know is:   Have others experienced waterhammer in their pumped condensate return lines (PCR) where high pressure traps discharge into the PCR, and, did the hammer go away when:

  1. They removed flash steam from  numerous blowing traps entering the PCR, or 
  2. They installed heat removal devices in Vaults to reduce the flash steam before in entered the PCR.

Alternately, did waterhammer not go away when they installed spargers or some other blending device in the HP trap assemblies entry to the PCR?

 

Write me a reply if you applied some fix for waterhammer in your PCR, and IT EITHER STOPPED WATERHAMMERING that was occurring before the fix,  OR it did not stop the waterhammer that it was supposed to prevent.   I’m trying to confirm that what I think is going on is actually what’s going on.  

 

Wayne Kirsner, P.E.

kirsner consulting engineering, inc.

www.kirsner.org 770-953-8262


From: wayne kirsner [mailto:kir...@kirsner.org]

Sent: Thursday, March 13, 2014 10:40 PM

To: 'Molnar, John'; 'distribut...@googlegroups.com'
Cc: 'Len Phillips'
Subject: RE: {Distribution Forum} Abridged summary of distribut...@googlegroups.com - 4 Messages in 1 Topic

 

John--I guess the tank would be full of liquid condensate.  My reasoning is that when the trap last cycled off (assuming it’s an on/off trap like a inverted bucket), the tank would be mostly full of flash steam.  As the flash steam condensed due to heat loss thru the vessel’s walls, it’s pressure would fall below that of the condensate return so condensate would push back into the tank and fill it (assuming no check valve between the tank and CR line).  When the trap next discharged, it would be putting flash steam into the condensate from above the condensate.  I agree this will not hammer, especially if condensate has not had time to subcool.

 

I guess the bottom line is—Does it work, meaning specifically, did it end waterhammer in the condensate return where you had it before

 

And, since the tank is effectively a condensate cooler, do you think it’s more cost effective than mounting a finned tube heat changer on the wall of the manhole and running the trap’s discharge thru it?

 

 