Control systems methods to monitor & control remote DE sites

4 views
Skip to first unread message

Len-IDEA

unread,
Jun 29, 2017, 12:01:11 PM6/29/17
to Distribution Forum
Posted on behalf of IDEA Member Karen Hinkforth, Senior Engineer at We-Energies:

Our district energy system consists of 13 miles of steam pipe. Steam is supplied by a single cogeneration plant. The plant’s distributed control system monitors pressures at the ends of the system and moves valves at various control stations to maintain pressure. Communication with the remote sites is by leased telephone lines.  The telephone company has informed us that they will soon discontinue support for these lines . What communication methods are other district energy systems using to control and monitor their systems? Can you recommend a vendor?

 

Karen Hinkforth

Senior Engineer – Power Generation

We Energies

office:  414-221-4133

karen.h...@we-energies.com

Edward T. Borer Jr.

unread,
Jun 29, 2017, 1:42:09 PM6/29/17
to Len-IDEA, Distribution Forum

We pull remote pressures, temperatures, and flows from a central Building Energy Management system and transfer key information via analog I/O to our energy plant SCADA system. This avoids IT security risk to the plant.  We do this for data gathering only. We do not use this strategy for _control_ of remote devices. Most (all?) of our steam pressure let-down stations are manually, locally adjusted.

 

Ted Borer, PE, CEM, LEED AP

Princeton University

Energy Plant Manager

MacMillan Building, Elm Drive

Princeton, NJ 08543-2158

Ph:(609) 258-3966

Fx:(609) 258-2298

Cell: (609) 731-2327

Home: (609) 466-3322

etb...@princeton.edu

 

Scientific evidence for warming of the climate is unequivocal.

Intergovernmental Panel on Climate Change

http://climate.nasa.gov/evidence/

 

“It would go a long way to caution and direct people in their use of the world, that they were better studied and knowing in the Creation of it. For how could [they] find the confidence to abuse it, while they should see the great Creator stare them in the face, in all and every part of it”

William Penn, 1693

--
You received this message because you are subscribed to the Google Groups "Distribution Forum" group.
To unsubscribe from this group and stop receiving emails from it, send an email to distribution-fo...@googlegroups.com.
To post to this group, send email to distribut...@googlegroups.com.
Visit this group at https://groups.google.com/group/distribution-forum.
For more options, visit https://groups.google.com/d/optout.

Hugh Bahar

unread,
Jul 5, 2017, 9:45:55 AM7/5/17
to Len-IDEA, Distribution Forum

The phone company should give a reasonable and customary amount of time for the plant to design and implement a solution.  Ask them for a quote to provide support for the lines until the plant can design and implement a new communication path. Cutting off control-critical phone service necessary to an operating plant invites a court injunction. 

 

Consider taking over the lines from the phone company if there is telecom copper between the control valves and plant.  If there isn’t a copper path that is entirely onsite, work with the phone company to determine if the onsite circuits can be bridged so most of the copper infrastructure can be maintained.

 

If copper can’t be maintained long-term, hire a company to establish a secure VPN via Ethernet between the valves and the plant.  Depending on how many control valves there are this could take a while.  If possible, run conduit from the control valves to the nearest local building, hopefully to an Ethernet connection in a mechanical room.  Control integrity, reliability, security and local/node room UPS & emergency power should all be paramount whether you continue with copper or move to Ethernet.  Every powered switch/actively powered component between the control valve and plant will need UPS/emergency power.

 

If I had to guess, rapid steam load changes swing this plant's boilers around.  If this is correct, a different control paradigm could be investigated  whereas it might be possible to eliminate the field-located control valves that are the concern.

 

If the IDEA member needs some communications savvy engineers, they may email me privately.

 

Regards,

Hugh


Hugh Bahar, PMP

President
Bahar and Associates, Inc.
4 Sunset Drive
Lansing, New York  14882
607-592-2197

Somrah, Dowlatram

unread,
Jul 5, 2017, 9:45:55 AM7/5/17
to Len-IDEA, Distribution Forum