You should not need anything else in the R installation. Make sure you install it in the default location.
I am not sure of your issue on vents. The example you gave would start with the vent closed but immediately open it slowly over 30 seconds to fully open at 30 s and then immediately start closing it over 30 seconds to fully closed at 60 s. Was that the intent? Normally we open/close vents over a 1 s interval. The shorter the interval the more rapid changes are and the slower CFAST will run through that interval. So a vent we want to open at 60 s would be F= 0, 0, 1, T = 0, 60, 61. Shorter or longer time opening/closing periods can be used.
I believe F_nnn just refers to the different time opening pairs, i.e., in you example F_1 = 0, F_2 = 1, F_3 =0. If that doesn’t seem correct give me a page number and manual you are looking at so I can check.
Paul
--
You received this message because you are subscribed to the Google Groups "CFAST" group.
To unsubscribe from this group and stop receiving emails from it, send an email to
cfast+un...@googlegroups.com.
To view this discussion on the web visit
https://groups.google.com/d/msgid/cfast/71221c91-3734-461c-a993-4fab26a4e135n%40googlegroups.com.