OK, thanks. Just another question to make sure I do the right thing:The vertikal flow vents in the programm are the vents on the sides of the compartment (like inlets for the air), aren't they? And the vertical flow vents are the vents that connect the top of the building to the outside (like smoke flues)? Or is it the other way round?
I am realy not sure if I implemented the location of the vents correctly, because in CFST there are just a few parameters that describe the location. For ex. for the vertical flow vents I can't specifiy the detailed location. So I guess just the sum of the vent surface is important, not where exactly they are located. For the horizontal flow vents the parameters Sill, Soffit and Width can be used to describe the location of the vent. But I am not sure what the reference point is. For example, if my Vent is located at the front and 2 m away from the left corner, then I use a vent offset of 2 m, right? And when I give a width of 40 m in addition that means that my went goes from 2 m to 42 m?
I attached my CFAST-file and a screenshot of the compartment. Can you check if the parameters I took make sense or if they are completely nonsense? Or is that too much effort?Also I don't need to give a smoke yield. Does CFAST take an average value for that or is there a way to implement that.Refering to the fire description: As the normal vector of the fire I used x=0. y=0 and z=1, because I thought that this makes sense, if the fire "looks up". In the User's Manual I don't find any clear statements refering to these questions.
OK, so an example to make it clear:
I want to position my horizontal flow vent on the front side 3 m away of the left corner of the front side. It is 2 m high, starts from the very bottom of the compartment (my building). The width of the vent (from the left side to the right side) is 4 m.
Then I use the follwing settings:
First compartment: Compartment X (my building), Vent offset: 3 m
Second Compartment: Outside (so I guess this is the environment of the building, so basically air), Vent offset: 3 m
Sill: 0 m
Soffit: 3 m
Width: 4 m
If I want the vents to open 10 s in delay: Initial opening fraction: 0, change fraction at: 10s, final opening fraction: 1
Wind Angle: 0 ° (no WInd)