Increased HGL temperatures between Version 7.3.1 and 7.4.3

46 views
Skip to first unread message

Burkhard

unread,
Aug 2, 2022, 5:44:51 PM8/2/22
to CFAST
Hello,

I use CFAST over a long time and from time to time repeat certain simulations like the reproduction of the standard fire curve in the UL of a given compartment.

I realized that between CFAST Versions 7.3.1 and 7.4.3 the HRR to reproduce the standard fire curve decreased by about more than 20%.
In other words, with the same HRR the compartment temperature significantly increased between Version 7.3.1 and 7.4.3.
In the release notes I could only find information on bugs regarding the target temperature calculation, not about the calculation of the ULT.

Could it be that anything was changed that impacted the ULT?

Kind Regards
Burkhard



Kevin McGrattan

unread,
Aug 2, 2022, 5:58:14 PM8/2/22
to cf...@googlegroups.com
Can you post the input file? We'll have to do a bisect on the versions.

Richard Peacock

unread,
Aug 3, 2022, 9:30:50 AM8/3/22
to CFAST
Between 7.3.1 and 7.4.3, there were fixes for vent opening and closing and secondary fire ignition, but nothing that should intrinsically change the ULT.  V&V results didn't show significant changes in ULT.

We'll need to look with your input file.

Burkhard Forell

unread,
Aug 5, 2022, 7:44:27 PM8/5/22
to cf...@googlegroups.com

Hi Richard and Kevin,

thank you for your feedback!

I am sorry, I found out that I was wrong with my first e-mail.

Instead, the significant temperature jump already happened between v 7.2.1 and 7.2.2.
I attach one input file and two output files from v 7.2.1 and  v 7.2.2.

Probably you are already aware of that change (It took me a little bit longer).

Kind Regards
Burkhard

--
You received this message because you are subscribed to the Google Groups "CFAST" group.
To unsubscribe from this group and stop receiving emails from it, send an email to cfast+un...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/cfast/036344c1-d7e0-41e5-87df-2c3bec5697d7n%40googlegroups.com.
2400m2_1a_F1.in
721_2400m2_1a_F1_n.xlsx
722_2400m2_1a_F1_n.xlsx