Dear Fazil,
I made a mistake and my input file was not opened correctly. The vents are setup correctly as well.
Now, I am being able to ran your case successfully. For your concern in smoke spread, CFAST provides output quantities: ULOD and LLOD (with unit of mass) in the _m.csv and ULOD and LLOD (with unit of reciprocal meter) in the _zone.csv.
You mentioned that the smoke concentration distribution is illogical. Can you further clarify what you mean by that?
Wall connection is used when you want to facilitate conductive heat transfer for surfaces between compartments.
Zone approximation: CFAST allows you to have one-zone approximation and two-zone approximation for a compartment in a simulation. One assumption in zone approximation (i.e. one-zone) is that mixture medium (air in the compartment) is well mixed within the compartment. This means that species concentration at any location in the compartment will be the uniform. From experimental studies, it is observed that there are normally two distinct gas layers (hot and cold) in a fire scenario at the fire developing stage. In order to better capture this effect, two zone approximation is used. In general, the upper gas layer is hot and more sooty and the lower gas is cooler and less sooty. For that, you will have to make a decision to choose which approximations best fits your case.
Sorry for the confusion from the previous email.
Thanks,
Andy