Hi,
i am a little bit confused, because in a other post describes a
complete different way of calculating the entrainment. It states that
if the fire is in the lower layer, the entrainment is calculated from
the top of the mean flame height to the interface layer. When the fire
is in the upper layer, is the distance between the base of the fire
and the ceiling. And so, there is a connection between the flame
height und the plume.
So, I tried to understand the process with your very good
documentation, but I don’t get the point.
So I tried to use a little example, maybe, the situation is clear
than.
I hope someone can give me answer.
So I have a Room, 20 meters width, 10 meters deep and 5 meter height.
There is a fire located in the middle of the room with a HRR of 900
kW. The area is 0.2 m².
So I try to make the plume Calculation by Hand. First, I see that
there a two formulas used. In the documentation the correlation from
Hesekstad is the fowling:
Me = 0.071 * Qf,c^1/3*(z-z0)^5/3+(1+0.026*Qfc^2/3*(z-z0)^-5/3)
In all other documentation I found the correlation is state as :
Me = 0.071 * Qf,c^1/3*(z-z0)^5/3 + 1.92*10^-3 * Qf,c
And there is a other correlation if z is below the Mean flame height.
The correlation in CFast is net valid below z=1 because its incorrect
for a negative base with a rational exponent if the exponent is odd.
Maybe I make a mistake in some way, but that is what I spot.
If a use the MacCaffey correlation the flaming region is up to 1.2
meters, the intermitted from 1.2 to 3 meters. So, my mind the reaction
is finished there and the plume begins to clam up. So the Plume begins
a 3 meters.
After 20 seconds the interface layer is at 4.26 meters.
So I try to calculate the air entrainment.
I build up an Integral from the correlation used in CFast with the
boundaries 3.06 and 4.26 because I think that’s the entrainment
region.
CFast states that there is a entrainment of 6.45 kg/s. I don’t
understand this value, because the result from my calculation is much
higher. I am complete wrong with my way ?
So, CFast works very well and so I try to understand where my
failure is
Thankyou
Sven
On 11 Okt., 21:00, CFAST Development <
cfast...@gmail.com> wrote:
> In a "real" fire, I'm sure there is a connection between the flame
> height,entrainment, and other plume properties. In CFAST though,
> there is no direct connection. The flame height calculation is just a
> side calculation done at the time of the creation of the printout. In
> CFAST, the plume calculation determines how much oxygen is available
> for combustion. While the correlation has an implied dependence on the
> fire size (by virtue of the heat release rate) and flame height (which
> has a role in determining the steady burning, intermittent burning, or
> plume region of McCaffrey's correlation for example), the flame height
> is not used in the actual calculation, just the emperical plume
> correlations. In the lower layer, theentrainmentis determined by
> the net heat release rate constrained by the available entrained
> oxygen (an iterative calculation). In the upper layer, theentrainmentis driven by the heat introduced by the lower layer
> burning plus any burning which can take place due to air entrained
> from the upper layer. Thus, the plume calculation is indeed used in
> both layers.
>
> To attempt to answer your specific questions:
>
> 1) There is no exact number, per se, where the model cannot be used.
> Certainly, a very large fire in a compartment, as would be indicated
> by large flame height, is an indication that care should be taken in
> using the model. However, there are a number of post-flashover fire
> examples in the validation tests for CFAST, quite often with excellent
> results.
>
> 2) Most typically, the fire will not descend totally below the base
> of the fire as specified by the user since someentrainmentmust take
> place to transfer mass and energy into the upper layer in the model.
> Thus, for fires high in a compartment, again, care should be taken in
> using the model. There is little is any experimental data for
> validation of fire high in a compartment.
>
> 3) The plume in CFAST is used in both layers. For McCaffrey's plume,
> for example, an appendix to the journal article referenced in the
> technical reference guide specifically details how this is done.
>
> 4) The 'Fire in Lower' and 'Fire in Upper' are simply the amount of
> heat released by the fire due toentrainmentin the lower layer
> > > standard plume correlation is used to calculateentrainmentof air
> > > into the plume that is then transported to the upper layer. If there
> > > is not enough oxygen entrained to completely burn all the fuel mass,
> > > this unburned fuel is also transported to the upper layer where is may
> > > burn if there is sufficient oxygen in the layer and if the temperature
> > > is above the specified volatilization temperature. When the layer
> > > descends lower than the base of the fire (again not related to the
> > > flame height calculation), then there is no lower layerentrainment
> > > and only the upper layer combustion takes place. An additional source
> > > of combustion takes place at vents withentrainmentcalculated as if
> > > - Zitierten Text anzeigen -- Zitierten Text ausblenden -