I have two thoughts, a general one and a more specific one that I can't fully answer without looking at your actual test case.
In general, CFAST, like all zone models, represents the environment in a compartment with two temperatures, one for the relatively hot upper gases and one for the relatively cooler lower gases. Thus all else being equal, all the detectors see the same lower layer temperature and thus react the same.
More specifically, CFAST does include algorithms to estimate the plume temperature when the location of a detector or target is closer to a fire location. I've attached a sample CFAST output the shows the calculated local temperatures in a slice across the compartment.
Far away from the fire in the middle of the compartment, the temperatures all take the value of the layer temperature. So, depending on how big your fire is and how far the detectors are from the fire, they could see elevated temperatures or just the layer temperatures. To understand more, we'd have to see your individual CFAST input file.
Richard Peacock
Hellothanks for the quick answer.My test room is in the data file, so maybe you can look inside.I would like to know when (point in time) my tmperature is rising up to 50 degree at a height of 2,50m, but not close to the fire location. In my test room are a lot of heat detectors at a height of 2,50n horizontal and vertically.I deduce from your answer that the programm CFSAT can´t resolve my problem?
One thing is seldom realting to your answer....my lower layer temperature is not the same temperature of my heat detectors at a height of 2,50m?