Issue 46 in cfast: Followup on Vent Area Limit Documentation

10 views
Skip to first unread message

codesite...@google.com

unread,
Oct 5, 2009, 4:53:24 PM10/5/09
to cfast-...@googlegroups.com
Status: New
Owner: ----
Labels: Type-Defect Priority-Medium

New issue 46 by allan.co...@wsms.com: Followup on Vent Area Limit
Documentation
http://code.google.com/p/cfast/issues/detail?id=46

The response to issue 19 was: “Our intention was to insure that the vent
does not get too large in relation to the room size. A ratio of the room
volume to vent area (not the other way around) of about 2 m is now used in
the documentation.”

The current text (SP 1026, April 2009) is: “In a single compartment, the
ratio of the area of vents connecting one compartment to another to the
volume of the compartment should not exceed roughly 2 m.”

The units in the current SP 1026 do not seem consistent. Is a revision to
the text planned?

--
You received this message because you are listed in the owner
or CC fields of this issue, or because you starred this issue.
You may adjust your issue notification preferences at:
http://code.google.com/hosting/settings

codesite...@google.com

unread,
Oct 6, 2009, 3:04:58 PM10/6/09
to cfast-...@googlegroups.com
Updates:
Status: Done
Labels: Component-Docs

Comment #1 on issue 46 by cfastdev: Followup on Vent Area Limit
Documentation
http://code.google.com/p/cfast/issues/detail?id=46

You're correct. The manual is still wrong. I've changed the document and
it will be reflected in the next official
update. The text has been changed to

In a single compartment, the ratio of the volume of the compartment to the
area of vents connecting the
compartment to another should not exceed roughly 2 m.

codesite...@google.com

unread,
Oct 6, 2009, 3:13:28 PM10/6/09
to cfast-...@googlegroups.com

Comment #2 on issue 46 by cfastdev: Followup on Vent Area Limit
Documentation
http://code.google.com/p/cfast/issues/detail?id=46

Fixed in revision 186