Issue 34 in cfast: CFAST fails if target position is listed as -1 in the input file

1 view
Skip to first unread message

codesite...@google.com

unread,
Oct 28, 2008, 1:36:03 PM10/28/08
to cfast-...@googlegroups.com
Issue 34: CFAST fails if target position is listed as -1 in the input file
http://code.google.com/p/cfast/issues/detail?id=34

New issue report by cfastdev:
If an input file contains a target location (X, Y, and/or Z) of -1 (the
default value that should equate to the center of the room), CFAST fails
at initialization. Normally, the GUI takes care of this so most users
will never see this problem (you have to manually edit a target to include
the -1).


Issue attributes:
Status: Accepted
Owner: cfastdev
Labels: Type-Defect Priority-Medium Component-Logic

--
You received this message because you are listed in the owner
or CC fields of this issue, or because you starred this issue.
You may adjust your issue notification preferences at:
http://code.google.com/hosting/settings

codesite...@google.com

unread,
Oct 28, 2008, 1:45:08 PM10/28/08
to cfast-...@googlegroups.com
Issue 34: CFAST fails if target position is listed as -1 in the input file
http://code.google.com/p/cfast/issues/detail?id=34

Comment #1 by cfastdev:
Corrected in Revision #54. Location is initialized to center of compartment
at the
floor when -1's are found in the location input.


Issue attribute updates:
Status: Verified

codesite...@google.com

unread,
Oct 28, 2008, 1:53:11 PM10/28/08
to cfast-...@googlegroups.com
Issue 34: CFAST fails if target position is listed as -1 in the input file
http://code.google.com/p/cfast/issues/detail?id=34

Comment #2 by cfastdev:
Output for targets with correctly specified positions verified as
unchanged. Sample
problem with -1s for target position (created manually) now works.