Dear BRICK Community,
First of all, thank you for a great open-source initiative which benefits the smart building industry.
Our company is working on development of a platform for data analytics and predictive energy optimization of buildings. We are connecting to existing BMS, running grey-box models in a cloud, and actively control HVAC systems. To enhance replicability, we decided to go BRICK for creating building typologies and mapping BACnet points. For the cases when some registers are not represented in the recent ontology, we are planning to create custom sub-classes on top of existing structures.
To begin with, as a new BRICK user I have a few questions/proposals related to the classification of certain data-points, and would be grateful if someone could address it here. Please let me know, what would it be the preferable communication approach - shall I post similar questions here, or use GitHub issues instead?
# related to AHU & hot water distribution system
1. Calculated dT (BACnet type 'AV', shows difference between the setpoint and actual value of process variable, e.g. discharge air temperature sensor/setpoint). Which BRICK point should I use for this?
2. delta-T threshold for activating & deactivating control loop. (BACnet type 'AV', 'degreesCelsius', specifies threshold to generate/abolish heating/cooling requests sent to downstream control elements, e.g. if supply temp. setpoint minus supply temp. measurement is higher than "threshold" → activate a certain control loop: heating coil/or heat wheel). Would "differential temperature setpoint" be applicable here, or it implies only for difference between two measurements (e.g. discharge/return air temperature sensor)? Or maybe "deadband temperature setpoint" is more suitable here?
3. Return Air Temperature Low/High Reset Setpoint. Currently, the sub-classes for reset setpoints include registers for DAT/OAT/HWST. However, some of the BMS systems contain control blocks with a control for discharge temperature based on return air temperature.
4. Hot Water Return Temperature Setpoint (located on return pipe of a heating coil, used for freeze protection). Ontology includes "supply/discharge water temperature setpoints" but does not have "return temperature setpoint".
5. Discharge Air Humidity Setpoint. There is a bit of inconsistency here: both humidity sensors and temperature sensors/setpoints have a list of sub-classes: discharge, outside, zone etc. Though, "humidity setpoint" is a lowest subclass in hierarchy.
6. Mixed Air Humidity Sensor is missing, while ontology includes a register for MAT sensor.
7. Intake Air Temperature/Humidity Sensor (located inside the supply duct of AHU). I couldn’t find it in the ontology. Typically, an OAT sensor is used for the whole building, while IAT sensors are AHU-specific.
8. Valve Position Sensor (BACnet type 'AV', 'percent', measures the current position of a valve as a fraction of its full range of motion). Ontology has "damper position sensor", but I don't see similar register for valves. Though, there is a register called "valve command". Would it be correct to use it also for read-only values?
9. Fan/Pump Flow Percentage (indicates % of maximum fan speed, or proportion of currently active units (e.g. if 3 out of 4 cascade units are active, then register indicates 75%)). There is a register called "motor speed sensor", but it does not cover 2nd case. Also "air/water flow sensors" are available, but in my understanding, it is more related to "measurable substance" rather than to equipment operation. Please correct me if I'm wrong.
10. VFD a) It seems the current description got mixed up ('An alarm that indicates a loss of water e.g. during transport'). b) Since it includes the subclass "Heat Wheel VFD", it would be logical to add "Pump VFD" & "Fan VFD".
11. Heating Valve. The description addresses only heating coil valve ('A valve that controls air temperature by modulating the amount of hot water flowing through a heating coil'). Is there a dedicated subclass for other heating valves in the hot water distribution system (e.g. three-way valve between primary/secondary hot water loops)?
12. Differential Pressure Bypass Valve. Also, I am not sure what is the best class for this? Maybe it should be included as a subclass of a water valve?
13. Hot/Chilled Water Supply Temperature Setpoint. Currently, the most granular class is the 'supply water temperature setpoint'. Would it be valuable to add sub-classes for hot/chilled water?
14. Min/Max Air/Water Temperature Setpoint Limit. At the moment, 'min temperature setpoint limit' has the only subclass 'min/max discharge air temperature setpoint limit'. Probably, it would be useful to add another subclass for e.g. 'min/max hot water supply (discharge) temperature setpoint limit'.
15. Filter has only one subclass - Mixed Air Filter. Additional sub-classes could be added to represent more AHU configurations: e.g. intake/return air filter.
# related to schedules
16. Time Program / Schedule (BACnet type 'SCH', represents operation schedule for a certain system (AHU, radiators, etc.))
17. Holiday Calendar / Schedule (BACnet type 'CAL', contains list of vacations, i.e. indicates days when mechanical system should be off)
18. Holiday Status (BACnet type 'BV', indicates whether today is holiday or not)
19. Overwork Button Command/Status (BACnet types 'BV/BI', activates system outside scheduled time) # probably can be captured by 'On Status' from the ontology
# some common modes that are used in BMS and are used for adjusting setpoints for discharge air temperature, or secondary hot water supply temperature
20. Compensation factor based on zone temperature (BACnet type 'AV', used for adjusting reset curves setpoints for discharge air/supply water based on real-time temperature feedback from a thermal zone). Typical registers include: status of compensation mode, reference zone temperature, increase/decrease offsets or parameters (it can be fixed or dT-based (if zone temperature is colder than reference, then increase supply temperature by "K1" , or by (Tref - Tzone) * "K2")), setpoints before/after compensation regulation. Are there relevant registers in the ontology to characterize this mode? If not, maybe it should be considered as an addition to "parameter class", as these compensation factors are pretty common in BMS.
21. Compensation factor based on wind speed (same principle as above, but wind speed sensor is used for adjusting reset curve setpoints)
22. Optimal startup mode (parameters, that can override startup time and temperatures for hot water distribution loop). Typical registers include: mode status, morning temperature offset (e.g. + 20 degrees on top of reset curve setpoint), step & time-delay parameters (to define how sharp and how long would it take for temperature to get back to normal operating conditions), zone setback temperature setpoint (if temperature drops at night below "T1", then heating system automatically activates), reference morning temperature & heating constant [minutes/degreeCelsius] (used to adjust morning startup time as follows: t_new = t_schedule - (T_ref - T_zone) * heating_constant). Similar questions - are there some registers in the ontology, that I can use to describe this mode? If not, would it be valuable to include it, and to what should be its hierarchical position?
23. Discharge Air Temperature Setpoint in various modes (specific registers to indicate "different stages of a setpoint" - based on reset curve only, reset curve + compensation factor, in optimal startup mode in the morning, actionable setpoint - that picks up highest value out of the above-mentioned "preliminary setpoints")
# equipment
24. Radiators. I cannot find radiators (equipment) in the ontology, though it was in 1.0.3 version as a subclass of 'terminal unit'. Currently, there are 'radiation hot water system' and 'water distribution', but it seems to system-level points rather than points to characterize individual equipment. Was it intentional decision to remove radiators from terminal units or was it overlooked?
# relationships
25. What are the proper relationship types for specifying parameters?
Could you please elaborate on the following example to give an idea what type of relationships are meant to be used between control elements and parameters that specify their behavior. For instance:
"AHU" that serves "zone" has "heating coil" that contains "heating valve" which is controlled by "PID controller" (and has "PID parameters: gain/band/step/time"). Control variable is "valve command", process variable is "discharge air temperature", and target value for PV is "discharge air temperature setpoint". Heating coil is activated only when "dT threshold" is met for "delay parameter" time.
So how ideally these points should be related to each other?
Thanks a lot for answering my questions. Please let me know if we can contribute somehow to BRICK development.
Best regards,
Smart Building Engineer at Spectral
--