Hi everyone
For ascertaining the no of bore wells required, one should know the
water table capacity, time to recharge,
1. Water table capacity will give a fare idea about amount of water
available in the ground at what depth and spread. This will help to
ascertain amount of water that can be pumped continuously per hour
depending up on pump capacity
2. Any bore well will reduce the water pumping out after some time,
and it requires time to recharge...may be hours or a day. In case of
apartment we should look at recharge time with in hours. Since the
requirement will be too high.
To calculate the potable water required you can take roughly 200*4 for
2 bedrooms and 200*6 for 3 bedrooms and add additional 50 -100 lit per
flat for common purpose like cleaning, landscape etc...
So for a 300 flats at the ratio of 60:40 for 2 and 3 bedrooms you need
3, 18,000 liters per day. This need to be pumped in a span of 24
hours.
Assuming that you run the motors 2 times a day every time you should
have bore wells with capacity to supply approx 1, 59,000 lts.
Usually for apartments of this scale you should go for agricultural
bores that have a huge like the above. These are the same from which
the tanker guys/bwssb supplies the ground water to many apartments.
Regards
Ar.Praveen.N
Ardes Architects and Interior Designers
ardesar...@yahoo.co.in