Statusdisplay
The Terminal Equipment Controller features a two-line, eight-character display. There is a low level backlight level that is always active and can only be seen at night.
When left unattended, the Terminal Equipment Controller has an auto scrolling display that shows the actual status of the system. There is an option in the configuration menu to lockout the scrolling display and to only present the room temperature and conditional outdoor temperature to the user. With this option enabled, no local status is given of mode, occupancy and relative humidity.
Each item is scrolled one by one with the back lighting in low level mode. Pressing any key will cause the back light to come on to high level. When left unattended for 10 seconds after changes are made, the display will resume automatic status display scrolling.
To turn on the back light to high level, press any key on the front panel. The back lit display will return to low level when the Terminal Equipment Controller is left unattended for 45 seconds
Unoccupied mode override
An Override can be made during an unoccupied period. If the Override option is enabled in the lockout configuration pressing the Override but-ton will resume occupied setpoints for a time specified by parameter ToccTime .
Mode button menu sequence
Modes presented to the user are dependent on the sequence of operation selected.
Default mode is shown in bold when sequence of operation parameter is changed.
System mode function
PLEASE NOTE THAT: Default system mode of operation is dependent on sequence of operation selected
Default mode is in bold when sequence of operation parameter is changed
The available mode can only be changed through the network since there is no local mode access
This parameter will only appear when a wireless network adapter is present. If the Terminal Equipment Controller is installed as a stand-alone (Network Ready) unit or with a BACnet or Echelon adapter, this parameter will not be used or displayed.
This parameter (Personal Area Network Identification) is used to link specific Terminal Equipment Controllers to a single specific Schneider-Electric wireless gateway (VWG). For every Terminal Equipment Controller reporting to a gateway (maximum of 30 Terminal Equipment Controllers per gateway), be sure you set the SAME PAN ID value both on the gateway and the Terminal Equipment Controller(s).
This parameter (Channel) is used to link specific Terminal Equipment Controllers to specific Schneider- Electric wireless gateway(s) (VWG). For every Terminal Equipment Controller reporting to a gateway (maximum of 30 Terminal Equipment Controllers per gateway), be sure you set the SAME channel value both on the gateway and the Terminal Equipment Controller(s).
Entering a MAC address enables an automatic routine that automatically fetches all the required configuration properties of the current device from another already configured device and copies the same required configured property values.
If a value other than the default value of 255 is entered, user will then be prompted to exit the Configuration Menu thus leaving all other parameter configurations to be copied from the referenced Terminal Equipment Controller MAC address.
(Motion NO) or (Motion NC): Advanced PIR occupancy functions using a Normally Open (NO) or Normally Closed (NC) remote PIR motion sensor. Occupancy mode is now set as per the applied PIR function and configuration. Application information and examples are available in the document: APP-PIR-Guide-Exx. This document will provide the installers and system designers with detailed examples on applications, parameter configuration information, sequence of operation, troubleshooting, and diagnostic help required for the proper usage of the PIR accessory covers
(Window) EMS: Forces the system to disable any current heating or cooling action by the Terminal Equipment Controller. The mode stays the same and the current setpoints are the same Occupied setpoints. Only the outputs are disabled. There is a Door/Window alarm displayed on the Terminal Equipment Controller to indicate to the local tenant that the door/window needs to be closed for cooling or heating to resume.
With this sequence enabled, the occupancy is now dictated through those 2 inputs. Any motion detected will set the zone to occupied status. The zone will remain permanently in occupied mode until the door contact switch opens momentarily. The Terminal Equipment Controller will then go in stand-by mode. If more movements are detected, the occupied mode will resume. While the door is opened, any movements detected by the remote PIR sensor or the PIR accessory cover will be ignored. Use a Normally Closed contact switching device.
(RemOVR): temporary occupancy remote override contact. This function disables the central button over- ride function on the Terminal Equipment Controller. The override function is now controlled by a manual remote momentarily closed contact. When configured in this mode, the input operates in a toggle mode. It is now possible to toggle between unoccupied & occupied setpoints for the amount of time set by parameter (TOccTime) temporary occupancy time.
(Filter): a backlit flashing Filter alarm will be displayed on the Terminal Equipment Controller LCD screen when the input is energized. It can be tied to a differential pressure switch that monitor filters
(Service): a backlit flashing Service alarm will be displayed on the Terminal Equipment Controller LCD screen when the input is energized. It can be tied in to the AC unit control card, which provides an alarm in case of malfunction.
The factory value or 0.0 hours: Setting this parameter to its default value of 0.0 hours disables the unoc- cupied timer. This prevents the Terminal Equipment Controller to drift from stand-by mode to unoccupied mode when PIR functions are used
Note that the default value of 3.0 F (1.2 C) gives satisfactory operation in most normal installation cases. The use of a proportional band different than the factory one is normally warranted in applications where the
Terminal Equipment Controller location is problematic and leads to unwanted cycling of the unit. A typical example is a wall mounted unit where the Terminal Equipment Controller is installed between the return and supply air feeds and is directly influenced by the supply air stream of the unit.
Our products are not only superior in quality, but so is the service our partners provide, enabling our customers to maximize their investment and future-proof their site. To deliver this exceptional experience, our partners gain access to a library of online and facilitated training material, and are supported by a team of team of knowledgeable technical support analysts and engineers.
This installation manual provides instructions and technical specifications for physical installation of the Protege DIN Rail Cellular Modem. For programming and operating information, see the Protege DIN Rail Cellular Modem Configuration Guide.
This configuration guide provides programming instructions and operating information for the Protege DIN Rail Cellular Modem. For installation instructions and technical specifications, see the Protege DIN Rail Cellular Modem Installation Manual.
This installation manual provides instructions and technical specifications for physical installation of the tSec Multi-Technology Card Reader. For programming information, see the ICT Card Reader Configuration Guide.