single Scan retries after timeout

91 views
Skip to first unread message

Arturas Paulius

unread,
Sep 30, 2021, 9:57:14 PM9/30/21
to opendnp3

Hello, Is there a way to stop single user defined scan retrying
to poll after timeout?

ms(1632941898328) WARN    Testas1 - Timeout waiting for response
ms(1632941944302) WARN    Testas1 - Link status request - response timeout
ms(1632941958342) INFO    Testas1 - Begining task: Disable Unsolicited
ms(1632941958342) --AL->  Testas1 - C6 15 3C 02 06 3C 03 06 3C 04 06
ms(1632941958342) --AL->  Testas1 - FIR: 1 FIN: 1 CON: 0 UNS: 0 SEQ: 6 FUNC: DISABLE_UNSOLICITED
ms(1632941958342) --AL->  Testas1 - 060,002 - Class Data - Class 1 - all objects
ms(1632941958343) --AL->  Testas1 - 060,003 - Class Data - Class 2 - all objects
ms(1632941958343) --AL->  Testas1 - 060,004 - Class Data - Class 3 - all objects
ms(1632941968351) WARN    Testas1 - Timeout waiting for response
ms(1632942004318) WARN    Testas1 - Link status request - response timeout

I need scan to stop, because other scans added to the same master are blocked. Is it possible to disable scans bind to the IMaster  ?

Adam Crain

unread,
Sep 30, 2021, 10:02:22 PM9/30/21
to opendnp3
Hi Arturas,

The message you've provided isn't a scan (READ request for data) it's the master asking the outstation to disable unsolicited reporting.

A conformant outstation should at least be able to respond to this request with the FUNC_NOT_SUPPORTED IIN bit.

That said, you can stop the master from sending disable/enable unsolicited messages via configuration:


Adam

Arturas Paulius

unread,
Oct 1, 2021, 10:46:55 AM10/1/21
to opendnp3
Thank you for responce,

disabling these messages helped

Arthur.