NFPA 13 Loading Dock Canopy

504 views
Skip to first unread message

Duane Miller

unread,
Feb 4, 2020, 11:31:51 AM2/4/20
to arkansasl...@googlegroups.com, arkan...@googlegroups.com

Opinions please

 

A loading/unloading area at a self-storage facility. Does it meet the definition of short-term transient?

 

Yes or No

 

 

A.5.3.2 Ordinary hazard occupancies (Group 2) include occupancies having uses and conditions similar to the following:

 

·         Exterior loading docks

 

Note that exterior loading docks only used for loading and unloading of ordinary combustibles should be classified as OH2.

 

A.8.15.7.5 Short-term transient storage, such as that for delivered packages, and the presence of planters, newspaper machines, and so forth, should not be considered storage or handling of combustibles. The presence of combustible furniture on balconies for occupant use should not require sprinkler protection.

 

 

 

Duane Miller

Fire Marshal Division – Fire Inspector/Plans Review

Bentonville Fire Department

Office: (479)271-3108

https://www.bentonvillear.com/214/Fire-Department

 

 

 

 

 

From: arkansasl...@googlegroups.com [mailto:arkansasl...@googlegroups.com] On Behalf Of Rumsey, Bill
Sent: Tuesday, January 28, 2020 1:46 PM
To: arkan...@googlegroups.com; arkansasl...@googlegroups.com
Subject: AFMA NFPA AGENDA SPRING 2020

 

IMPORTANT UPDATE…Attached is the agenda for the Spring 2020 meeting in Jacksonville. Ben Hammond will be sending out registration for the NFPA Safety Summit soon. Please notice special instructions for booking at the bottom of the agenda. Questions, please call myself or Jake Feemster (479) 271-5547.

 

 

--
You received this message because you are subscribed to the Google Groups "ArkansasLifeSafety" group.
To unsubscribe from this group and stop receiving emails from it, send an email to arkansaslifesaf...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/arkansaslifesafety/c4047fe5b84c44d1b02db80120f057c0%40rogersar.gov.

Scott Lacey

unread,
Feb 4, 2020, 2:23:36 PM2/4/20
to arkansasl...@googlegroups.com, arkan...@googlegroups.com

Good question Duane.   I tend to lean towards No, since this area is specifically intended to loading/unloading of bulk combustibles.  This would be like a loading dock on the back of a store.  Not like a UPS truck pulling up to a hotel once a day, or individuals unloading luggage.

 

Questions I would consider on benefit of sprinklers:

  • Is canopy of non-combustible construction as required by NFPA 13 to omit sprinklers
  • Restriction of egress – Are there adequate exits if this is blocked
  • Is it tied into the main building or is there a gap or overlap for heat to escape
  • Height of canopy and if heat will reach sprinklers over the fire

 

 

 

Scott Lacey, PE, CSP, SFPE

Fire Protection Engineer / President

 

Fire prot engineering logo small

 

Registered PE in AR and AZ.

 

Sc...@LaceyFPE.com

(501) 679-1753

P.O. Box 723

Greenbrier, AR 72058

 

Confidentiality Statement: This email may include confidential information that shall not be duplicated, used, or disclosed outside of the person or persons named above either in whole or in part for any purpose.  If you have received this transmission in error, please immediately notify us and destroy the transmission.