No. |
Document/ Drawing No. |
Comments |
Contractor Reply |
|||
|
1 |
Slide no 11 |
1.Please attach the material specification for epoxy to be used. As per construction drawing chemical adhesive will be RE 500 or equivalent. 2. To attach PE endorsed drawing of proposed precast segment. |
|
|||
|
2 |
Slide 12 and 13 |
1.Statement 8 and 9 are duplicated.
2.Please state what will be the depth (shaded in yellow) once the precast segment slotted and levelled against the existing footpath. 3.Material to be used for casting the connection point? Non-shrink grout? Please attach the material specification of non-shrink grout. |
|
|||
|
3 |
Slide 18
|
1.What is the length of starter bar shown. 2.Top surface of wall to be roughened prior proceed the second cast of top slab. 3.To show the strut details to support the wall. |
|
|||
|
4 |
Precast Segments |
1.Understand that the precast segments were fabricated differ in length i.e. 0.85m,0.95m and 1m to suit the existing ground level, please indicate on the plan drawing where will be these segments to be installed for reference. 2.To submit lifting plan for both unloading and installation of precast segment. |
|
|||
|
5 |
Site verification |
1.To verify minimum allowable soil bearing pressure on existing ground is 95kPa. |
|
|||
|
6 |
TCP |
1.The signages indicated on the TCP are not following the code of practice for traffic control at work zone. Please revise the advanced warning signages at both Park Street and Straits View (ref LTA COP).
2.The cones and lateral shift marker for lane closure should be placed between Straits View and Marina way. |
|
Dear all,
Please see the revised method statement for URA CST as attached, together with the corresponding RA and TCP.
Thank you.
Regards,
GUI Geyi
Deputy Project Manager
Or Kim Peow Contractors (Pte) Ltd
No.30 Tagore Lane
Singapore 787484
M:96259166
Email: gui...@okph.com
From: Shiela ANG (LTA) <Shiel...@lta.gov.sg>
Sent: Friday, 11 April 2025 4:43 pm
To: Gui GeYi <gui...@okph.com>
Cc: Kance Liong <kance...@okph.com>; Zufri WAHAB (LTA) <Zufri...@lta.gov.sg>; Nurul Ain ABDUL RAZAK (LTA) <Nurul_Ain_...@lta.gov.sg>; Francis Edward Iglesia Angad <franci...@okph.com>; Vinci Ma Huai En <vin...@okph.com>; Vellaiyan Balamahendra
Muniappa <vell...@okph.com>; Cordelia Herbert <cord...@okph.com>; Than Than Soe <thant...@okph.com>; Ligu YANG (LTA) <YANG...@lta.gov.sg>; Nathanael FOO (LTA) <Nathan...@lta.gov.sg>; Patrick MAGLALANG (LTA) <Patrick_...@lta.gov.sg>; Neary
Clevan Medolin <nearyclev...@gmail.com>; Gian Karlo Antalan <ant...@okph.com>; Tinni Lar Tun <tinni...@okph.com>; Parayno Gladys Joy Cayabyab <parayn...@okph.com>; Kee Nam Eng <keen...@okph.com>; Vinci Ma Huai En <vin...@okph.com>
Subject: RE: AM201 - Park Street - Method Statement for URA CST
Hi Geyi,
Please revise the Method Statement for Park St as discussed yesterday.
Additionally, please revise the TCP to follow similar format as attached.
Thank you.
Best Regards,
Shiela
From: Gui GeYi <gui...@okph.com>
Sent: Tuesday, 8 April 2025 5:05 pm
To: Shiela ANG (LTA) <Shiel...@lta.gov.sg>
Cc: Kance Liong <kance...@okph.com>;
Zufri WAHAB (LTA) <Zufri...@lta.gov.sg>;
Nurul Ain ABDUL RAZAK (LTA) <Nurul_Ain_...@lta.gov.sg>;
Francis Edward Iglesia Angad <franci...@okph.com>;
Vinci Ma Huai En <vin...@okph.com>;
Vellaiyan Balamahendra Muniappa <vell...@okph.com>;
Cordelia Herbert <cord...@okph.com>;
Than Than Soe <thant...@okph.com>;
Ligu YANG (LTA) <YANG...@lta.gov.sg>;
Nathanael FOO (LTA) <Nathan...@lta.gov.sg>;
Patrick MAGLALANG (LTA) <Patrick_...@lta.gov.sg>;
Neary Clevan Medolin <nearyclev...@gmail.com>;
Gian Karlo Antalan <ant...@okph.com>;
Tinni Lar Tun <tinni...@okph.com>;
Parayno Gladys Joy Cayabyab <parayn...@okph.com>;
Kee Nam Eng <keen...@okph.com>;
Vinci Ma Huai En <vin...@okph.com>
Subject: RE: AM201 - Park Street - Method Statement for URA CST
Dear Shiela,
Please see our revised method statement with the TCP as shown in the link below:
(20250408) URA CST Method Statement (at Park Street).pptx
Thank you.
Regards,
GUI Geyi
Deputy Project Manager
Or Kim Peow Contractors (Pte) Ltd
No.30 Tagore Lane
Singapore 787484
M:96259166
Email: gui...@okph.com
From: Gui GeYi
Sent: Thursday, 3 April 2025 2:08 pm
To: 'Shiela ANG (LTA)' <Shiel...@lta.gov.sg>
Cc: Kance Liong <kance...@okph.com>;
Zufri WAHAB (LTA) <Zufri...@lta.gov.sg>;
Nurul Ain ABDUL RAZAK (LTA) <Nurul_Ain_...@lta.gov.sg>;
Francis Edward Iglesia Angad <franci...@okph.com>;
Vinci Ma Huai En <vin...@okph.com>;
Vellaiyan Balamahendra Muniappa <vell...@okph.com>;
Cordelia Herbert <cord...@okph.com>;
Than Than Soe <thant...@okph.com>;
Ligu YANG (LTA) <YANG...@lta.gov.sg>;
Nathanael FOO (LTA) <Nathan...@lta.gov.sg>;
Patrick MAGLALANG (LTA) <Patrick_...@lta.gov.sg>;
Neary Clevan Medolin <nearyclev...@gmail.com>;
Gian Karlo Antalan <ant...@okph.com>;
Tinni Lar Tun <tinni...@okph.com>;
Parayno Gladys Joy Cayabyab <parayn...@okph.com>;
Kee Nam Eng <keen...@okph.com>;
Vinci Ma Huai En <vin...@okph.com>
Subject: RE: AM201 - Park Street - Method Statement for URA CST
Dear Shiela,
Please see our revised method statement for Park Street as attached for your review.
Regarding your reinforcement details, we will follow the construction drawings. Please see the drawings as attached. However, we will be unable to backfill the portion under the constructed footpath for the pre-cast sections due to the construction method.

Additionally, we will also not be able to remove the formwork for the cast insitu method of construction.
Please see the endorsed drawings for the precast segments and the lifting details.
Please do let me know should you have any additional queries.
Thank you.
Regards,
GUI Geyi
Deputy Project Manager
Or Kim Peow Contractors (Pte) Ltd
No.30 Tagore Lane
Singapore 787484
M:96259166
Email: gui...@okph.com
From: Shiela ANG (LTA) <Shiel...@lta.gov.sg>
Sent: Wednesday, 2 April 2025 2:25 pm
To: Gui GeYi <gui...@okph.com>
Cc: Kance Liong <kance...@okph.com>;
Zufri WAHAB (LTA) <Zufri...@lta.gov.sg>;
Nurul Ain ABDUL RAZAK (LTA) <Nurul_Ain_...@lta.gov.sg>;
Francis Edward Iglesia Angad <franci...@okph.com>;
Vinci Ma Huai En <vin...@okph.com>;
Vellaiyan Balamahendra Muniappa <vell...@okph.com>;
Cordelia Herbert <cord...@okph.com>;
Than Than Soe <thant...@okph.com>;
Ligu YANG (LTA) <YANG...@lta.gov.sg>;
Nathanael FOO (LTA) <Nathan...@lta.gov.sg>;
Patrick MAGLALANG (LTA) <Patrick_...@lta.gov.sg>;
Neary Clevan Medolin <nearyclev...@gmail.com>;
Gian Karlo Antalan <ant...@okph.com>;
Tinni Lar Tun <tinni...@okph.com>;
Parayno Gladys Joy Cayabyab <parayn...@okph.com>;
Kee Nam Eng <keen...@okph.com>;
Vinci Ma Huai En <vin...@okph.com>
Subject: RE: AM201 - Park Street - Method Statement for URA CST
Hi Geyi,
Please see our comments as attached.
Thank you.
Best Regards,
Shiela
From: Gui GeYi <gui...@okph.com>
Sent: Friday, 28 March 2025 3:38 pm
To: Shiela ANG (LTA) <Shiel...@lta.gov.sg>
Cc: Kance Liong <kance...@okph.com>;
Zufri WAHAB (LTA) <Zufri...@lta.gov.sg>;
Nurul Ain ABDUL RAZAK (LTA) <Nurul_Ain_...@lta.gov.sg>;
Francis Edward Iglesia Angad <franci...@okph.com>;
Vinci Ma Huai En <vin...@okph.com>;
Vellaiyan Balamahendra Muniappa <vell...@okph.com>;
Cordelia Herbert <cord...@okph.com>;
Than Than Soe <thant...@okph.com>;
Ligu YANG (LTA) <YANG...@lta.gov.sg>;
Nathanael FOO (LTA) <Nathan...@lta.gov.sg>;
Patrick MAGLALANG (LTA) <Patrick_...@lta.gov.sg>;
Neary Clevan Medolin <nearyclev...@gmail.com>;
Gian Karlo Antalan <ant...@okph.com>;
Tinni Lar Tun <tinni...@okph.com>;
Parayno Gladys Joy Cayabyab <parayn...@okph.com>;
Kee Nam Eng <keen...@okph.com>;
Vinci Ma Huai En <vin...@okph.com>
Subject: AM201 - Park Street - Method Statement for URA CST
Dear Shiela,
As discussed, please see the method statement (powerpoint) for Park Street near Marina One in the link as shown below, for your comments if any. The PDF file is attached for your reference.
As communicated previously, we will use the cast in-situ construction method at the tapering locations.
With your no objections, we will proceed to send it to URA CST for approval to start works.
Thank you.
Regards,
GUI Geyi
Deputy Project Manager
Or Kim Peow Contractors (Pte) Ltd
No.30 Tagore Lane
Singapore 787484
M:96259166
Email: gui...@okph.com
Hi Geyi,
As discussed during the meeting earlier, please see further comments below:
Please also follow up on Neary’s comments below.
Thank you.
Best Regards,
Shiela
Hi Shiela,
We have coordinated with Certis, URA CST’s inspection team for a site inspection on 5 May 2025 at 9am before we commence work on site.
Please see our reply as shown below, regarding your earlier comments:
As discussed during the meeting earlier, please see further comments below:
Please also follow up on Neary’s comments below.
|
No. |
|
Document/ Drawing No. |
Comments |
Contractor Reply |
|
1 |
Slide no 11 |
1.Please attach the material specification for epoxy to be used. As per construction drawing chemical adhesive will be RE 500 or equivalent. 2. To attach PE endorsed drawing of proposed precast segment. |
|
1. MF-EX2. Please see material specification as attached. 2. Please see PE endorsed drawing as attached |
|
2 |
Slide 12 and 13 |
1.Statement 8 and 9 are duplicated.
3.Material to be used for casting the connection point? Non-shrink grout? Please attach the material specification of non-shrink grout. |
|
1. Noted. Amended. 2. Noted. Amended. 3. Yes, non-shrink grout is to be used. Please see the material specification as attached. |
|
3 |
Slide 18
|
1.What is the length of starter bar shown. 2.Top surface of wall to be roughened prior proceed the second cast of top slab. 3.To show the strut details to support the wall. |
|
1&2. Noted. Amended. 3. Not required. Please see detailed method statement in link.
|
|
4 |
Precast Segments |
1.Understand that the precast segments were fabricated differ in length i.e. 0.85m,0.95m and 1m to suit the existing ground level, please indicate on the plan drawing where will be these segments to be installed for reference. 2.To submit lifting plan for both unloading and installation of precast segment. |
|
1. Please refer to lifting plan as attached |
|
5 |
Site verification |
1.To verify minimum allowable soil bearing pressure on existing ground is 95kPa. |
|
Noted. Please see detailed method statement in link. |
|
6 |
TCP |
1.The signages indicated on the TCP are not following the code of practice for traffic control at work zone. Please revise the advanced warning signages at both Park Street and Straits View (ref LTA COP).
2.The cones and lateral shift marker for lane closure should be placed between Straits View and Marina way. |
|
As the area before the work zone (between Straits View & Marina View) is only 45m, we are unable to strictly follow the COP for traffic control at the work zone.
|
Thank you.
Regards,
GUI Geyi
Deputy Project Manager
Or Kim Peow Contractors (Pte) Ltd
No.30 Tagore Lane
Singapore 787484
M:96259166
Email: gui...@okph.com
From: Shiela ANG (LTA) <Shiel...@lta.gov.sg>
Sent: Wednesday, 16 April 2025 4:37 pm
To: Neary Clevan Medolin <nearyclev...@gmail.com>; Gui GeYi <gui...@okph.com>
Cc: Kance Liong <kance...@okph.com>; Zufri WAHAB (LTA) <Zufri...@lta.gov.sg>; Nurul Ain ABDUL RAZAK (LTA) <Nurul_Ain_...@lta.gov.sg>;
Francis Edward Iglesia Angad <franci...@okph.com>; Vinci Ma Huai En <vin...@okph.com>; Vellaiyan Balamahendra Muniappa <vell...@okph.com>;
Cordelia Herbert <cord...@okph.com>; Than Than Soe <thant...@okph.com>; Ligu YANG (LTA) <YANG...@lta.gov.sg>; Nathanael FOO (LTA)
<Nathan...@lta.gov.sg>; Patrick MAGLALANG (LTA) <Patrick_...@lta.gov.sg>; Gian Karlo Antalan <ant...@okph.com>;
Tinni Lar Tun <tinni...@okph.com>; Parayno Gladys Joy Cayabyab <parayn...@okph.com>; Kee Nam Eng <keen...@okph.com>; Ayyakannu
Ramachandran <ayya...@okph.com>; Zulkarnain Bin A Rahman <zulka...@okph.com>; Chua Hock Beng <chuahock...@yahoo.com.sg>;
am20...@googlegroups.com
Subject: RE: AM201 - Park Street - Method Statement for URA CST
Hi Geyi,
As discussed during the meeting earlier, please see further comments below:
Please see our reply to Neary’s comments below.
|
No. |
Document/ Drawing No. |
Comments |
Contractor Reply |
|
1 |
Slide no 11 |
1.Please attach the material specification for epoxy to be used. As per construction drawing chemical adhesive will be RE 500 or equivalent. 2. To attach PE endorsed drawing of proposed precast segment. |
|
1. MF-EX2. Please see material specification as attached. 2. Please see PE endorsed drawing as attached |
|
2 |
Slide 12 and 13 |
1.Statement 8 and 9 are duplicated.
3.Material to be used for casting the connection point? Non-shrink grout? Please attach the material specification of non-shrink grout. |
|
1. Noted. Amended. 2. Noted. Amended. 3. Yes, non-shrink grout is to be used. Please see the material specification as attached. |
|
3 |
Slide 18
|
1.What is the length of starter bar shown. 2.Top surface of wall to be roughened prior proceed the second cast of top slab. 3.To show the strut details to support the wall. |
|
1&2. Noted. Amended. 3. Not required. Please see detailed method statement in link. |
|
4 |
Precast Segments |
1.Understand that the precast segments were fabricated differ in length i.e. 0.85m,0.95m and 1m to suit the existing ground level, please indicate on the plan drawing where will be these segments to be installed for reference. 2.To submit lifting plan for both unloading and installation of precast segment. |
|
1. Please refer to lifting plan as attached |
|
5 |
Site verification |
1.To verify minimum allowable soil bearing pressure on existing ground is 95kPa. |
|
Noted. Please see detailed method statement in link. |
|
6 |
TCP |
1.The signages indicated on the TCP are not following the code of practice for traffic control at work zone. Please revise the advanced warning signages at both Park Street and Straits View (ref LTA COP).
2.The cones and lateral shift marker for lane closure should be placed between Straits View and Marina way. |
|
As the area before the work zone (between Straits View & Marina View) is only 45m, we are unable to strictly follow the COP for traffic control at the work zone.
|
Hi Shiela,
Please see our amended TCP as shown in the link below:
As discussed, we would very much appreciate your assistance in helping to apply for the ERIMS permit so that we can close the lane to facilitate our works at Park Street.
Hi Geyi,
Please see the notification number for the above-mentioned location for construction of cycling path.
Reminder to update the following inside the WhatsApp group :-
Please also ensure to update LTA prompt prior to lane closure and update BusOps.

Thank you.
Best Regards,
Shiela