Honeywell Vista 20P - Reprogramming to allow entry/exit delay for backdoor.

123 views
Skip to first unread message

cra...@gmail.com

unread,
Aug 10, 2017, 2:52:55 PM8/10/17
to
Can someone confirm or advise whether what I am thinking of doing will work for my Vista 20P Honeywell alarm system.

Desired outcome: add a delayed entry/exit for a backdoor(leaving the front door on a delayed entry as well)

Current configuration:
Residential home currently programmed with 8 zones.

Front door is on zone 2 by itself, currently programmed as type 01 zone with delayed entry/exit.

Backdoor and kitchen & Porch windows are on Zone 3 (which currently does not allow for a delayed entry of the backdoor)


Based on the Youtube videos I've watched and reading of various manuals/sites. I am thinking that if I merely reprogram Zone 3 to a type 02 or 03 zone this will allow for delayed entry/exit from the Backdoor. I am assuming the kitchen windows would also be on the delay since they are wired in zone 3 along with backdoor but I'm not concerned about them being on the delay too.

So will this work? or because the windows being on same zone as backdoor will this create a problem other than them being delayed too that I am not aware of?

Note: No motion sensor concerns as not within path to backdoor.

Thank you for your help
CF



RTS

unread,
Aug 10, 2017, 6:10:04 PM8/10/17
to
02 will make it a entry 2 ( be sure and set the amount of time your
want at * 36)
Exit time will be same for both...