Back when I was a Simplex Tech I would place in the program an equation that
would among other things "disable" the horn/strobe ckts, the city connect and
fire doors on a warm or cold start to pervent accidental alarms from inproperly
installed devices, could this be what is happining?
FYI I also always created a "psuedo" trouble that was held on panel and city
trouble until I had "un-disabled" (is that a word?) the 1st program as a
reminder that things were still disabled.
Dan
Have you checked for a reverse polarity position of a horn cct.?
Are all horn ccts installed with properly sized EOL resistors?
I would remove all horn ccts, install and EOL resistor on all associated
terminals and see if the panel then clears. If it clears then the problem is
definitely field related and not part of the control panel. How about wiring
? Is the field horn ccts sized appropriately so as not to allow for too much
V drop to the EOL devices, check it.
Good luck.
Northshore Contracting