Thank you for any assistance. I tried to find AIP on the web but couldn't
locate them.
Sincerely,
Ken
"Ken Abrahamsen" <kabra...@aol.com> wrote in message
news:V9sza.992621$S_4.1008691@rwcrnsc53...
No problem... Most heat detectors are normally open devices and have to be
wired in parallel with each other then supervised by an end of line (as the
last device in the circuit)... An alarm condition causes a dead short
across the zone. An "open" (broken wire/disconnected detector) will cause a
trouble.
That's most likely a private labeled Edwards 281B. The unit is a
rate-of-rise detector with a 135ºF fixed temperature sensor as well. It
detects a rapid increase in temperature typical of a fast-burning, flaming
fire. These are often used in places where smoke detectors are not
permitted, such as enclosed furnace rooms, laundry rooms, kitchens and
garages. There is some difference of opinion among installers as to whether
to use them in kitchens and garages due to the potential for a rapid
temperature increase.
The rate-of-rise part of the sensor is self-restoring. The fixed thermal
sensor is sacrificial. Once it reaches 135ºF the detector must be replaced.
The connection is simple enough. These sensors are open circuit. That is,
they close on alarm. There are two screw terminals on each side of the
sensor. Connect the fire alarm zone loop (also called an Initiating Device
Circuit, or IDC) to two of the screw terminals. Connect the EOL resistor or
the wires leading to the next detector to the other two screws.
For an explanation of fire alarm circuits, EOL resistors and other stuff,
you may wish to browse my FAQ site.
Regards,
Robert
=============================>
Bass Home Electronics
www.Bass-Home.com
2291 Pine View Circle
Sarasota, FL 34231
877-722-8900 Sales & Support
941-232-0791 Mobile
=============================>
> The connection is simple enough. These sensors are open circuit. That
is,
> they close on alarm. There are two screw terminals on each side of the
> sensor. Connect the fire alarm zone loop (also called an Initiating
Device
> Circuit, or IDC) to two of the screw terminals. Connect the EOL resistor
or
> the wires leading to the next detector to the other two screws.
Another piece of bad advice... EOL resistors must be mounted on a separate
plate on most commercial/industrial/institutional settings... In a
residential setting this usually doesn't apply, but then this guy hasn't
given you any indication on what type of application this is or even where
he's located (Canada, US, Belgium...)...
>
> For an explanation of fire alarm circuits, EOL resistors and other stuff,
> you may wish to browse my FAQ site.
Which has several errors and ommissions (particularly pertaining to fire
alarm applications)... Contact your local AHJ to find out what codes or
standards apply to your installation, Ken...
Keep trying. You're wrong of course, but feel free.
>> For an explanation of fire alarm circuits, EOL resistors and other stuff,
>> you may wish to browse my FAQ site.
>
> Which has several errors and ommissions (particularly pertaining to fire
> alarm applications)... Contact your local AHJ to find out what codes or
> standards apply to your installation, Ken...
It's easier to bad-mouth my site than build your own, eh Frank?
Code reference? NFPA says nothing of the sort. NEC doesn't discuss it.
Perhaps there's something different in Canada, but I'm in the US. Any
information I give is intended for a US audience. People living in other
countries should check with their local authorities.
>> For an explanation of fire alarm circuits, EOL resistors and other stuff,
>> you may wish to browse my FAQ site.
>
> Which has several errors and ommissions (particularly pertaining to fire
> alarm applications)...
That's an easy claim to make but not so easy to back up. State what is
erroneous and back up your claim with code reference. Otherwise it's just
more of your usual BS.
> Contact your local AHJ to find out what codes
> or standards apply to your installation, Ken...
Regards,
ULC CAN4-S524 Standard for Installation of Fire Alarm Systems... Yes, it's
a "Canadian" code... Since UL and ULC will be "merging" shortly, I figure
there's a good chance your guys will be having a good hard look at a more
stringent standard and adopting it. If EOL plates are "unheard" of in your
neck of the woods why would manufacturers be selling them???
>
> >> For an explanation of fire alarm circuits, EOL resistors and other
stuff,
> >> you may wish to browse my FAQ site.
> >
> > Which has several errors and ommissions (particularly pertaining to fire
> > alarm applications)...
>
> That's an easy claim to make but not so easy to back up. State what is
> erroneous and back up your claim with code reference. Otherwise it's just
> more of your usual BS.
Nope... I'm not in the business of helping the single most disruptive
participant in this newsgroup with "fixing" his FAQ... You picked out one
of the errors though... but, just one... Hopefully anyone with a lick of
sense that's interested in installing his own system will take the advice so
many have already posted (and that is to check out their local building
codes and AHJ before following the mis-information posted on some online
store's FAQ)...
Side note: I notice you no longer promote the one major "approval" you've
worked so hard over the years to get... ASA Online Vendor... You've never
been able to take any sort of criticism without immediately thinking it's an
"attack" or "flame".
Request: If you're going to be posting more of your "flocked-up" FWA's
(Frequently Wrong Advice) kindly post them in plain text for those of us
who've disabled HTML on our newsreader... I'd hate to miss out on another
good chuckle...
If I was in Canada my post would not have applied to commercial fire alarm
systems. Since I live in the US and service DIY'rs (not commercial fire
systems) your response was entirely inappropriate.
> Yes, it's a "Canadian" code... Since UL and ULC will be "merging"
> shortly...
Something you only learned from me.
> I figure there's a good chance your guys will be having a good
> hard look at a more stringent standard and adopting it.
Even if the merger does take place there are different requirements for
commercial fire alarms from residential systems. I've only a passing
interest in commercial fire alarms. You have zero experience with either
since all you do is sell parts at a distributor in Vancouver.
> If EOL plates are "unheard" of in your neck of the
> woods why would manufacturers be selling them???
Perhaps they're real popular in Nova Scotia. Next time I drive up to Canada
I'll have to check.
> > >> For an explanation of fire alarm circuits, EOL resistors and other
> stuff,
> > >> you may wish to browse my FAQ site.
> > >
> > > Which has several errors and ommissions (particularly pertaining to
fire
> > > alarm applications)...
> >
> > That's an easy claim to make but not so easy to back up. State what is
> > erroneous and back up your claim with code reference. Otherwise it's
just
> > more of your usual BS.
>
> Nope... I'm not in the business of helping...
Translation: You lied. There are no errors on the referenced page. In
fact, my information on fire alarms is directly from NFPA ( a book you
really ought to read some time).
> the single most disruptive participant in this newsgroup...
That would be you.
> with "fixing" his FAQ... You picked out one of the errors though... but,
just one...
You claim there are lots of errors but refuse to say where. Uh-huh. You're
full of crap.
> Side note: I notice you no longer promote the one major "approval" you've
> worked so hard over the years to get... ASA Online Vendor...
The owner of that website has reverted to posting nothing but ads and
blatant personal attacks. I don't support that sort of behavior.
> You've never been able to take any sort of criticism without
> immediately thinking it's an "attack" or "flame".
Constructive criticism involves correction. You attack and post nothing of
value.
> ...kindly post them in plain text for those of us...
Request denied.
--
"Frank Olson" <Use_the_e...@alt-security-alarms.com> wrote in message
news:zNwza.60095$Vi5.1...@news1.calgary.shaw.ca...
> Another piece of bad advice... EOL resistors must be mounted on a
separate
> plate on most commercial/industrial/institutional settings... In a
> residential setting this usually doesn't apply, but then this guy hasn't
> given you any indication on what type of application this is or even where
> he's located (Canada, US, Belgium...)...
so then how do know its bad advise Frank?
Marc Mazzarese
ABC Alarm Holdings
Aquisitions
Robert Answered:
The owner of that website has reverted to posting nothing but ads and
blatant personal attacks. I don't support that sort of behavior.
Mike Said:
Robert, lets not start this shit rolling. **YOU** are the one who started
promoting yourself (as Usual) **YOU** were asked by many to stop posting links
to your site and to post them to the manufacturers websites. **YOU** started
posting what you call FAQ's, 99.67% which are wrong, outdated, misleading,
incomplete and wrong. I asked you to be part of the ASA online vendors to prove
a point to myself as well as the group. I knew that it would just be a matter
of time for you to go against it and do things your way again. I wanted the
group to see that the problem here was not me but **YOU**. Robert, from this
moment on in my book you do what you like. I have to say, Jake, Jim, Frank and
the others were right. You are, and always will be one miserable person. You
will never change.
Mike, Sr.
32 Years in the trade
http://www.AlarmServicesInc.com
Online Store
http://www.AlarmSuperStore.com
ASA online vendor
FREE Shipping $ 100.00 or More
All others just===> $5.95
Simple... before he "spouts" off an answer he should be checking to see
*where* the poster is, and what kind of installation he's looking at
(residential, commercial, etc.). I take it when someone calls you on the
phone and asks a similar question of you, you just rattle off an answer
without first asking what the app is? It's bad advice if the answer's not
properly qualified...
Did you ask where the poster was located before spewing out your answer??
Did you ask what kind of application he's working on???
>
> > Yes, it's a "Canadian" code... Since UL and ULC will be "merging"
> > shortly...
>
> Something you only learned from me.
Nope... But keep on guessing...
>
> > I figure there's a good chance your guys will be having a good
> > hard look at a more stringent standard and adopting it.
>
> Even if the merger does take place there are different requirements for
> commercial fire alarms from residential systems. I've only a passing
> interest in commercial fire alarms. You have zero experience with either
> since all you do is sell parts at a distributor in Vancouver.
:-) I sell, service, install, and verify fire alarm systems, access
control, cctv, and security (mostly commercial these days)...
>
> > If EOL plates are "unheard" of in your neck of the
> > woods why would manufacturers be selling them???
>
> Perhaps they're real popular in Nova Scotia. Next time I drive up to
Canada
> I'll have to check.
The standard I quoted doesn't just apply to Nova Scotia... Keep twisting...
>
> > > >> For an explanation of fire alarm circuits, EOL resistors and other
> > stuff,
> > > >> you may wish to browse my FAQ site.
> > > >
> > > > Which has several errors and ommissions (particularly pertaining to
> fire
> > > > alarm applications)...
> > >
> > > That's an easy claim to make but not so easy to back up. State what
is
> > > erroneous and back up your claim with code reference. Otherwise it's
> just
> > > more of your usual BS.
> >
> > Nope... I'm not in the business of helping...
>
> Translation: You lied. There are no errors on the referenced page. In
> fact, my information on fire alarms is directly from NFPA ( a book you
> really ought to read some time).
Robert... Take Mike's advice and fix the last FAQ you posted... Don't
forget to give him the credit though...
>
> > the single most disruptive participant in this newsgroup...
>
> That would be you.
>
> > with "fixing" his FAQ... You picked out one of the errors though...
but,
> just one...
>
> You claim there are lots of errors but refuse to say where. Uh-huh.
You're
> full of crap.
Nope. Just refuse to help you...
>
> > Side note: I notice you no longer promote the one major "approval"
you've
> > worked so hard over the years to get... ASA Online Vendor...
>
> The owner of that website has reverted to posting nothing but ads and
> blatant personal attacks. I don't support that sort of behavior.
Yeah... right... so you've reverted back to posting erroneous FAQ's and
more links to your web site...
>
> > You've never been able to take any sort of criticism without
> > immediately thinking it's an "attack" or "flame".
>
> Constructive criticism involves correction. You attack and post nothing
of
> value.
Your FAQ's have no place in this group unless it's in response to a specific
question... Do simply post them does nothing but provoke negative responses
from other participants... That's your intention anyway, isn't it St.
Bass???...
>
> > ...kindly post them in plain text for those of us...
>
> Request denied.
Good... perhaps the individuals that come here looking for advice will see
what a total idiot you really are (and Jake, Mike, Graham, and others won't
have to point that out)...
>> Side note: I notice you no longer promote the one major "approval" you've
>> worked so hard over the years to get... ASA Online Vendor...
>
>The owner of that website has reverted to posting nothing but ads and
>blatant personal attacks. I don't support that sort of behavior.
>
I am still laughing at this.
Mr. Spam ad himself-
>
>> ...kindly post them in plain text for those of us that don't use HTML...
>
>Request denied.
>
Oh course
>Frank wrote to Robert Bass:
>> Side note: I notice you no longer promote the one major "approval" you've
>> worked so hard over the years to get... ASA Online Vendor...
>
>
>Robert Answered:
>The owner of that website has reverted to posting nothing but ads and
>blatant personal attacks. I don't support that sort of behavior.
>
>Mike Said:
>Robert, lets not start this shit rolling. **YOU** are the one who started
>promoting yourself (as Usual) **YOU** were asked by many to stop posting links
>to your site and to post them to the manufacturers websites. **YOU** started
>posting what you call FAQ's, 99.67% which are wrong, outdated, misleading,
>incomplete and wrong. I asked you to be part of the ASA online vendors to prove
>a point to myself as well as the group. I knew that it would just be a matter
>of time for you to go against it and do things your way again. I wanted the
>group to see that the problem here was not me but **YOU**. Robert, from this
>moment on in my book you do what you like. I have to say, Jake, Jim, Frank and
>the others were right. You are, and always will be one miserable person. You
>will never change.
>
Where's the other 46 people that put their names on the 'anti-bAss
list?"
Jake :-)
Just for the heck of it I reread NFPA72 and NEC looking for anything that
specifies a requirement for a separate plate for EOL resistors. There's not
only nothing there to support your contention. There is actually a diagram
showing the EOL mounted directly to the last device in the line -- precisely
what I recommended and precisely the opposite of what you said.
How can mounting an EOL on a plate as the last device on the loop be
precisely the opposite of what you said? You continuously refer to NEC (the
US standard). I refer to ULC CAN4-S524 (the Canadian one). The latter is
apparently much more stringent than NEC. It also requires a separate
verifying agency and report to sign off on any new installs or additions to
existing ones.
You never bothered asking the guy where he was located (US or Canada for
example). The UK standard is pretty tough too I hear and a whole lot
different from NEC in many respects. You *assume* everyone that asks a
question here is from the US, then give advice that could very well
contravene their own AHJ's. What you should be asking is... Is it a code
violation to mount the EOL on a separate plate (one that's designed for it)?
No.