Fire department came to inspect the dameg and told them they have 7 days to
get their sprinklers monitored.
I'm pretty sure it is grandfathered as not requiring them to be monitored,
but all that beig said, how do you get an electrical enginer to rubber stamp
a set of plans and pull a permit and get it installed all in seven (7) days?
--
Bob La Londe
http://www.YumaBassMan.com
Regards,
Robert L Bass
www.BassBurglarAlarms.com
"Bob La Londe" <use...@diycomponents.com> wrote in message
news:IoudnSYKIsR...@adelphia.com...
"Bob La Londe" <use...@diycomponents.com> wrote in message
news:IoudnSYKIsR...@adelphia.com...
I just dealt with an inspector yesterday and he wanted both, although he
admited the chain and lock were not required if tamper was monitored.
"Bob La Londe" <use...@diycomponents.com> wrote in message
news:89ydnZG0NamFe-Te...@adelphia.com...
The IBC requires all sprinkler water flow and valve position switches
(that may be tamper resistant) to be monitored. The only exceptions
being R-3 and limited sprinkler systems (fewer than 20 heads).
Several Arizona cities accept drawings submitted by a NICET III
certified technician.
Good luck!
Mike
--
Michael B. Baker, SET