We have had a couple recurring problems with this system.
It went into alarm once just after installation indicating an alarm with a
single pull station. The pull station had not been activated and there was
nothing wrong with the wiring to it.
At one time it locked up and locked up one of the phone lines regularly.
Firelite told us we needed a new EPROM for it which we got and installed.
We have had no problems for several months until about 3 days ago.
The system for no apparent reason went into alarm. It did not send any
signals. When I sent a service tech to the site the following day there was
nothing showing on the display, but the bell circuit was still buzzing
weakly. None of the devices had been tripped. It had locked up the phone
lines and the customer had unplugged the phone line jacks to clear up their
lines for use. The panel appeared to be locked up. He powered down and
powered back up the system and it appeared to operate correctly.
By looking at my central station record it appears to have had its
malfunction between the first and second auto test signals that it sends
every night.
I have not been back over the to do a complete test on the system, but it is
reporting auto test signals properly now. I received a call from the fire
department today. They want me to send them a letter guaranteeing this
system will work. I can't do that because is not the first time this panel
has locked up.
Power seems to be fine. Phone lines appear to be fine. What do I do.
I am getting very frustrated with this system. I am ready to rip it out and
install something else in its place. Everything is installed correctly and
when we check everything its all hooked up correctly and tests out properly.
There are only a handful of devices on this system. Its very easy to test
each circuit. There are:
Sprinkler flows and tampers
One smoke detector
One bell
One pull station
The Security Consultant
Bob La Londe - Owner
849 S Ave C
Yuma, Az 85364
(928)782-9765 ofc
(928)782-7873 fax
Check the date of manufacture on the board. FireLite must have had a "bad
batch". Order a new board and send the old one back for testing.
"Frank Olson" <Please-use-th...@yoursecuritysource.com> wrote in
message news:_yB2f.142505$1i.84226@pd7tw2no...
No, and we have had this conversation here before. Its not required to be
per NFPA. (Unless its changed in the last year) It must be wired to have
line siezure, and in this case there are two lines in use, both are properly
wired for line siezure. Some local jurisdictions (not this one) have
mis-interpreted the NFPA to say that it must be on a dedicated line but they
are wrong. As near as I have been able to determine only the CS receiver
lines must be dedicated which of course they are and in huge rotary line
groups. I believe that Phoenix is one of those who have said a FACP must
have dedicated lines.
--
> When I sent a service tech to the site the following day there was
>nothing showing on the display, but the bell circuit was still buzzing
>weakly.
Did you check the AC on the secondary of the x-former?
--
-Graham
Remove the snails to email
No. Are you thinking the transformer inside the panel is bad? Woudln't
that continuously be bad though? I mean a transformer is a pretty simple
device. Just a couple windings. Usually they either work or they don't.
--
"Bob La Londe" <use...@diycomponents.com> wrote in message
news:1128983099.79cb55ec3098acf62c7c0e026f71b708@teranews...
>> Did you check the AC on the secondary of the x-former?
>>
>
>No. Are you thinking the transformer inside the panel is bad? Woudln't
>that continuously be bad though? I mean a transformer is a pretty simple
>device. Just a couple windings. Usually they either work or they don't.
Yeah, they usually just work or don't work, but it may be under (or over)
voltage. I'm not sure what the secondary output is supposed to be on that
panel, it's just something that might be causing the glitches you've explained.
Did you check the voltages in troubleshoot mode?
MODE -> 8768 -> ENTER
Voltages can be viewed by performing the following steps:
• AC input voltage - press A and then the [ENTER/STORE] key
• Battery voltage - press B and then the [ENTER/STORE] key
• Zone 1 voltage - press 1 and then the [ENTER/STORE] key
• Zone 2 voltage - press 2 and then the [ENTER/STORE] key
• Zone 3 voltage - press 3 and then the [ENTER/STORE] key
• Zone 4 voltage - press 4 and then the [ENTER/STORE] key
• Zone 5 voltage - press 5 and then the [ENTER/STORE] key
• NAC #1 voltage - press b then 1 and then the [ENTER/STORE] key
• NAC #2 voltage - press b then 2 and then the [ENTER/STORE] key
• Resettable 24 volt power - press the RESET key and then the [ENTER/STORE] key
Either way it's the panel or the x-former causing the problems, I just wanted to
remind you to check the transformer before replacing the panel.
Good luck.
-G
"Bob La Londe" <use...@diycomponents.com> wrote in message
news:1128980965.d4efe6be779881e82ba5281c1ad6fa8c@teranews...
"Bob La Londe" <use...@diycomponents.com> wrote in message
news:1128980965.d4efe6be779881e82ba5281c1ad6fa8c@teranews...
As someone who works in a central station with several brands of receivers
accepting tens of thousands of signals a day that is absurd.
Any panel that locks up due to a CS receiver does is a panel I would have
nothing to do with
"Mark Leuck" <m..leuck@comcast.net> wrote in message
news:jNmdnRZwF42...@comcast.com...
How ever his last messenge the day before yesterday said.
"When a panel locks up, or if the lines stay latched or always on, it is
usually due to a non-UL listed receiver compatible with our panels. It is
quite common."
--
Bob La Londe
Cheapskate's Ways to Do Fishing Stuff
(The Frugal Fisherman)
Through the Month of October 2005
"Bob Worthy" <secu...@bellsouth.net> wrote in message
news:o0O3f.15619$5l....@bignews6.bellsouth.net...
Doug L
--
"Bob La Londe" <use...@diycomponents.com> wrote in message
news:7bqdnZH7I-q...@adelphia.com...
WHATTTTT??????
What panel have you EVER heard of that will lock up if it can't
communicate with the reciever? If it can't communicate, it hangs up and
tries again. JEEEEEEZ. Suppose this system was in an unoccupied
building? Duuuuh, it's just going to stay locked up until somebody
happens to notice it? How many service calls does it take to fix it?
Who pays for them? Firelite?
I'd tell them it's damn well time that they do something about it and
to get back to me when they do, so I can start buying their panels
again.
Then you can add, very politely, that you're going to help them in
their efforts by putting the word out on the various Internet trade
groups, that you participate in and at your alarm association meetings,
on a regular basis.
If you wanted to carry it further, you can write a letter to Firelite
president, outlining the problem, quoting the converstation and/or with
copies of e-mail messages, asking how they are going to address this
problem. Any referral to the problem in their reply will be an
acknowlegement that it exits.
After receipt, send a copy of the correspondence to the local and State
Fire Marshal, Underwriters and any of the other agencies that are on
Firelites approval list, with your comments on the problem, and CC a
copy to Firelite. The results won't be quick, but it will eventually be
corrected.
As long as no one complains and the panel has been listed and approved,
all Firelite has to do is keep putting it off with comments such as you
recieved.
I can't speak for Osborne-Hoffman receivers since I've never messed with one
but it still seems like a stupid suggestion by Fire-Lite's support.
Regardless of which format you are using and it doesn't matter if the the
two devices cannot communicate with each other at all that panel SHOULD NOT
lock up.
I've seen problems in the past with other manufacturer and in the end it's a
panel problem that later gets quietly fixed in the next BIOS revision. Of
course only AFTER that fix is in place do they bother to confirm the problem
existed.
I'm sorry but that is total bullshit, I have NEVER heard of a panel locking
up because of a receiver.
BTW What format are you using?
Exactly!
Umm I...hope you umm....took my name.....off ....it....?
:)
LOL. Mark Leuck said.... Yeah. I just cut pasted the message. No names
or headers. LOL.
CID
I may try 4 X 2 if I can't isolate the problem.
The tough part is I have done a complete inspection and test ont his panel
per NFPA four times now. Everything tests out just perfect.
Can't hurt but did FireLite say this (bogus) problem only happens with CID?
"Mark Leuck" <m..leuck@comcast.net> wrote in message
news:_cmdnbTTGP5...@comcast.com...
Hey I been around and know how things work, people complain then they
suddenly "go away"... know what I mean?
Not exactly, but the tech guy specificaly mentioned CID " Not every receiver
that is "Contact ID" compatible is going to work with every panel. " in one
of his e-mails. I figured there is a reason for that. He also suggested
using 4X2 " I would try other formats to see what works and is received fine
by the central station, something like 4+2 format." standard in another as
an option when I asked if siwtching to a pulse format would solve the
problem. Of course I had never told him what format I was using in the
first place so, I assumed there was a reason he mentioned CID specifically.
P.S. Remember the FBII XL-31. Has runaways with CID reporting. Switch
back to pulse 4 X 2 and it works just fine.
<shaking head> That still won't lock up a panel
The only time that could happen is between 10-digit and 4-digit CID
available on the Ademco 15/20P panels but not supported by Fire-Lite.
True but did that lock up the panel? No
The latest.
ME
The problem is it is not consistent. Its been almost three months since the
last problem with this panel. I have also ordered some phone line
suppressors just to be on the safe side.
THEM
Bob,
Let us know what the final outcome is.
Thanks
ME
Well, push come to shove you have a problem with this panel. I can see
communications problems, but there is absolutely no good reason for it to
lock up regardless.
P.S. This panel was installed this year and is most definitely still under
warranty.
THEM:
Bob,
If you look on the board, there should be a white sticker with a persons
name on it, with numbers (ex. Dawn S 4003), the first two digits represent
the week and the last two are the year it was manufactured, so the example
would be the 40th week of 2003. A year from that date is the warranty from
FireLite.
ME:
Interesting.
So you guys won't honor the warranty on a panel from the date of sale?
It didn't sit on my shelf, but I can't speak for the distributor.
Further comments.
We shall see what they say. They are now going out of their way to
prequalify it as probably not under warranty. Are things really that bad
over at Firelite?
--
> THEM:
> Bob,
>
> If you look on the board, there should be a white sticker with a persons
> name on it, with numbers (ex. Dawn S 4003), the first two digits represent
> the week and the last two are the year it was manufactured, so the example
> would be the 40th week of 2003. A year from that date is the warranty from
> FireLite.
The "warranty" issue should be handled by your distributor, and not between
you and FireLite. When you purchase a vehicle in September '05 that was
made in February 2005 the warranty starts from when you drive it off the
lot, not from the date it was made. The manufacturer's date is there to
identify specific issues with the hardware or firmware and has absolutely
nothing to do with the "in service" date or the day you buy it from Tried
(if however you purchased something from Tried and found out it was made in
1999, I'd take it back and give 'em hell!).
>
> ME:
> Interesting.
> So you guys won't honor the warranty on a panel from the date of sale?
> It didn't sit on my shelf, but I can't speak for the distributor.
>
> Further comments.
> We shall see what they say. They are now going out of their way to
> prequalify it as probably not under warranty. Are things really that bad
> over at Firelite?
Nope. You got a guy that didn't know what the heck he was talkin' about.
Heh, Tri-Ed pulls that shit with me now and then; pointing to the date on a
board as a warranty qualifier. (DSC)
js
I ran into that situation just once. Now I have them open the cans and
right the dates right on the invoice. The ULC panels have serial numbers on
them so it makes identifying specific panels easier but not completely
fool-proof (the serial number isn't on the board). The solution would
probably involve an extra step at the factory but if they did that with all
their units, there would be no argument.