I'm having a bit of a problem.....here it is.
Using an Ademco 20P, which has (1) 4219 Zone Expander ( I will be installing
2 more 4229 on top of that) installed.
Installed 3 System Sensor 2100AT two wire smoke detectors on the 4219
expansion board.
And it dont work (No blinking LED on the SD, no alarm triggers....Nothing!).
I then was told 2 wire smokes will not work on the expansion board, that
they have to be wired to zone 1 on the 20P Panel. Thats fine, but I wanted
my smokes on independent zones (Not all on one zone).
I was then told I'd be relegated to using 4 wire smokes if I want them wired
into the 4219 or 4229 expansion boards.
Anybody ever experience this? Is this correct?
Thanks,
Eddie
Eddie
"Jim Rojas" <jro...@tech-man.com> wrote in message
news:zd8C9.4130$Q27....@nwrddc01.gnilink.net...
> 2 wire smokes must go on zone 1 only. 4 wire smokes can go on any zone.
>
> Jim Rojas
>
> "Eddie" <lva...@worldnet.att.net> wrote in message
> news:yr6C9.19362$hK4.1...@bgtnsc05-news.ops.worldnet.att.net...
Jim Rojas
"Eddie" <lva...@worldnet.att.net> wrote in message
news:yr6C9.19362$hK4.1...@bgtnsc05-news.ops.worldnet.att.net...
Can't do it, they have to occupy zone 1 on the main board
> And it dont work (No blinking LED on the SD, no alarm
triggers....Nothing!).
> I then was told 2 wire smokes will not work on the expansion board, that
> they have to be wired to zone 1 on the 20P Panel. Thats fine, but I wanted
> my smokes on independent zones (Not all on one zone).
Sorry, wrong panel then
> I was then told I'd be relegated to using 4 wire smokes if I want them
wired
> into the 4219 or 4229 expansion boards.
>
> Anybody ever experience this? Is this correct?
You can use the 4-wire smokes on any zone but zone 1 however the power from
the smokes must wire into a relay on the 4219 to be able to reset the smokes
in the event of an alarm
If my 4 wire smoke is on zone 25, and it trips, and then initiates an
alarm, when I hit code + Off, this should reset the smokes
automatically....or so I thought. I dont believe a reversing relay is
necessary.......?
Am I ASSuming wrong?
Thanks,
Eddie
"m..leuck" <m.l....@attbi.com> wrote in message
news:xMeC9.78293$nB.5839@sccrnsc03...
Nope, while you do use code + off as the command without a relay it won't do
a thing, its not like the old Vista-10
>
You guys are correct....hooked it up last night, and no reset with code. Ah
well, live and learn.
Thanks for the help. Reversing relay, here we come.....
Eddie
"m..leuck" <m.l....@attbi.com> wrote in message
news:jRzC9.54907$P31.25661@rwcrnsc53...
The Vista-20P can have any zone programmed as a fire zone, zone 1 is for
2-wire and everything else can be 4-wire but you will need a 4204 relay to
reset the 4-wire
>
Eddie
"m..leuck" <m.l....@attbi.com> wrote in message
news:CtjE9.107119$WL3.49228@rwcrnsc54...
Thanks for letting me know this.....I will be checking this out for myself.
If this is true, Ademco has a HUGE potential Liabilty problem.
If you guys here in ASA that are "in the know", hear of a fix for this
problem, or a recall, (If in fact it is a real problem for all of the 4219
zone expanders), I would appreciate an e-mail.
This is crazy, they should have an instant recall or something for the zone
expanders.
So the way I read your e-mail, this problem does NOT happen if all of your
smokes and CO's are wired to the main panel? What happens to your burgs if
they go into trouble first? Will they not go into alarm then?
Thanks again,
Eddie
"Kevin E." <pan...@mts.net> wrote in message
news:pgcF9.2056$S87....@news1.mts.net...
> Sorry guys,
> I hope that you are not putting four wire smoke's on you 4219.
> I was hooking up a fire alarm trouble loop from a Co2 detector and noticed
> that if the Co2 went into trouble first and then alarm the 4219 would NOT
> recognize the alarm.
> Now we have to put all fire related equipment on the main board and burgs
on
> the zems.
> Ademco is aware of this problem.
>
> Kevin
>
>
> "Eddie" <lva...@worldnet.att.net> wrote in message
> news:m4uE9.31253$hK4.2...@bgtnsc05-news.ops.worldnet.att.net...
"Eddie" <lva...@worldnet.att.net> wrote in message
news:G5JG9.39736$hK4.3...@bgtnsc05-news.ops.worldnet.att.net...
I have not verified this, but will this weekend.
If this is true, it's going to be a major pain in the ass, lots of
re-programming to do, and shuffling around of a nice, neatly installed panel
with 3 zone expanders.