I'm installing a small simple DSC PC1550 alarm system. I only have
2 door sensors and a motion detector right now. My question is
- how do I tell the system that I'm not using zones 4,5 and 6?
The manual doesn't seem to be of any help. It suggests that all
6 zones need to be programmed but doesn't give an option for
disabling the zone.

Thanks in advance for any help you can give me.

kevin

-----------== Posted via Deja News, The Discussion Network ==----------
http://www.dejanews.com/ Search, Read, Discuss, or Start Your Own

VSS DOUG

unread,
Apr 9, 1999, 3:00:00 AM4/9/99
to
Kevin wrote

>how do I tell the system that I'm not using zones 4,5 and 6?
>The manual doesn't seem to be of any help. It suggests that all
>6 zones need to be programmed but doesn't give an option for
>disabling the zone.

If you have programmed the system for EOL resistors then on the 1550 you will
need to short out (common & the zone terminal) the unused zones using 1K
resistors, if you have programmed the system using NC loops then short out the
unused zones with a piece of wire. The zone definition of the unused zones is
not important although I like to program unused zones as slow,silent instant
(11).

Doug L

TracNo9

unread,
Apr 9, 1999, 3:00:00 AM4/9/99
to
Just program zones as any type and put end of line resistors at control board.