On Friday, January 1, 2016 at 10:38:04 PM UTC-5, Cmarti5 wrote:
Hello,
I would need more information from you as to what kind of controllers you are using to diagnose.
If you are using KT400's then it is always the locks shorting out the controllers, the KT400's use wet lock supply directly off the controller, if there is a potential to ground anywhere in the line it will bring down your 485 communications loop which shares a common ground.
If your using KT300's then the same problem exists.
KT200's i believe are form C relays for locks and dont suffer from this, thus why most people say they are rock solid, in all reality the 400's installed correctly will outlast any 200.
I digress, Make sure your panels have good batteries... as this would cause loop failures. If you are using a KTNCC make sure that it is sufficiently powered using the proper rated transformer 16/40AC, and the Battery is good otherwise remove any faulty batteries.
The fact that you see lock failure, or supervision tells me it has to do with locks right off the bat. replacing faulty locks will usually fix the issue.
HES1006 locks usually fail first due to the wiring inside the keeper warming up when doors on schedule or just the tension and rubbing.
You should have a trained professional look into your issues as this cannot be fixed by an enduser no matter how tech savvy.