It's impossible to answer that question without further
troubleshooting.
Have you used a program like Hyper-terminal to check the data string
at the controller end?
Have you tried pull-up resistors at the panel end on the data lines
0 and 1 yet?
1. What is the total distance of wire from reader to controller?
2. Is the wire shielded with the shield connected to the ground lug at
the central controller?
3. Did you use the correct gage wire?
3. Did that reader work reliably before?
I used to work for an access control manufacturer and a wiegand
extender was always recommended when interference was present. Another
option that I've seen work well in the field is a unit now made by
Schlage (or IR or whatever):
http://www.ir-swa.com/GEK.shtml
These are expensive, though.
Then there is "voltage drop" with long distances. Use a larger gauge wire
for long distances. Something which starts out as 5 volts on one end can be
2 volts at the other end!
Voltage drop calculator...
http://www.nooutage.com/vdrop.htm
Shielded cable...
http://images.google.com/search?q=Shielded+cable&hl=en&sa=N&um=1&ei=ixs-S8_8DIyGtAOlod0G&oi=images_breadcrumbs_list&ct=images-breadcrumbs-list&cd=1
"Dave White" wrote in message
"Dave White" <renof...@shaw.ca> wrote in message
news:%L7%m.30$nR4...@newsfe01.iad...
nope, what value of resistor? is it manufacturer specific?
"techie" <nor...@techie.com> wrote in message
news:hhmcu...@news3.newsguy.com...
"Effenpig1" <dirtysp...@hotmail.com> wrote in message
news:63fb6195-c23d-47b5...@u41g2000yqe.googlegroups.com...
I was just going by one install I did where 12 of the 36 readers
would not read a card correctly and they all happened to be the
readers that were farthest away. Our tech guru at our office said to
put some pull up resistors between the power and Data 0 and power and
Data 1 lines at the panel. Every reader was working after that.
I just happen to be going by the site tomorrow morning for remodel
work, I'll look at the resistor value. It's been 3 years since I did
it. It is a Lenel system with the Indala readers.
Gonna say it's either 1K or 4.7K resistors. I'll look when I get
there and post tomorrow.
What kind of system is it? Controller model? Brand and model of
reader?
cool, I am going to my site today, will try out some different resistor
values
Went by today, it was 4.7K resistors.
corrected the problem today.
I split up the wiegand wires onto different pairs.
works great now!
Usually set the baud rate at 9600 and leave the rest of the settings
default.Hyper terminal is great for determining that the data is being
sent properly before you start chasing ghosts. Kinda makes you regret
tossing those old windows 95 laptops with the serial port among other
reasons