>I had very similar symptoms with my 1994 4000 last year. My solution was to
>clean out the carburetor. I was told that this is a common problem caused
>by infrequent usage. I now run the gen set at least 15 minutes a month.
Fifteen minutes isn't much. I don't know about the 4000, but on my
2800 Microlite the manual specifically calls for an exercise period of
two hours or more every four weeks, under at least half load. This is
two hours of continuous running, not several shorter periods.
The reason for this is not only to reduce the fuel problems you
mentioned, but also to heat up the generator portion itself (not the
engine) enough to drive out accumulated moisture.
Suggest your check your manual if you have one.
GB in NC
My suggestion....take it to a professional before wasting money on
unnecessary parts...