24 CFR Part 3280
3280.808
Wiring methods and materials.
(a) Except as specifically limited in this part, the wiring methods
and materials specified in the National Electrical Code (NFPA No. 70-
1993) shall be used in manufactured homes.
(b) Nonmetallic outlet boxes shall be acceptable only with
nonmetallic cable.
(c) Nonmetallic cable located 15 inches or less above the floor, if
exposed, shall be protected from physical damage by covering boards,
guard strips, or conduit. Cable likely to be damaged by stowage shall be
so protected in all cases.
(d) Nonmetallic sheathed cable shall be secured by staples, straps,
or similar fittings so designed and installed as not to injure any
cable. Cable shall be secured in place at intervals not exceeding 4\1/2\
feet and within 12 inches from every cabinet, box or fitting.
(e) Metal-clad and nonmetallic cables shall be permitted to pass
through the centers of the wide side of 2-inch by 4-inch studs. However,
they shall be protected where they pass through 2-inch by 2-inch studs
or at other studs or frames where the cable or armor would be less than
1\1/2\ inches from the inside or outside surface of the studs when the
wall covering materials are in contact with the studs. Steel plates on
each side of the cable, or a tube, with not less than No. 16 MSG wall
thickness shall be required to protect the cable. These plates or tubes
shall be securely held in place.
(f) Where metallic faceplates are used they shall be effectively
grounded.
(g) If the range, clothes dryer, or similar appliance is connected
by metalclad cable or flexible conduit, a length of not less than three
feet of free cable or conduit shall be provided to permit moving the
appliance. Type NM or Type SE cable shall not be used to connect a range
or a dryer. This shall not prohibit the use of Type NM or Type SE cable
between the branch circuit overcurrent protective device and a junction
box or range or dryer receptacle.
(h) Threaded rigid metal conduit shall be provided with a locknut
inside and outside the box, and a conduit bushing shall be used on the
inside. Rigid nonmetallic conduit shall be permitted. Inside ends of the
conduit shall be reamed.
(i) Switches shall be rated as follows:
(1) For lighting circuits, switches, shall have a 10-ampere, 120-125
volt rating; or higher if needed for the connected load.
(2) For motors or other loads, switches shall have ampere or
horsepower ratings, or both, adequate for loads controlled. (An ``AC
general-use'' snap switch shall be permitted to control a motor 2
horsepower or less with full-load current not over 80 percent of the
switch ampere rating).
(j) At least 4 inches of free conductor shall be left at each outlet
box except where conductors are intended to loop without joints.
(k) When outdoor or under-chassis line-voltage wiring is exposed to
moisture or physical damage, it shall be protected by rigid metal
conduit. The conductors shall be suitable for wet locations. Electrical
metallic tubing may be used when closely routed against frames, and
equipment enclosures.
(l) The cables or conductors shall be Type NMC, TW, or equivalent.
(m) Outlet boxes of dimensions less than those required in Table
370-6(a) of the National Electrical Code (NFPA No. 70-1993) shall be
permitted provided the box has been tested and approved for the purpose.
(n) Boxes, fittings, and cabinets shall be securely fastened in
place, and shall be supported from a structural member of the home,
either directly or by using a substantial brace. Snap-in type boxes
provided with special wall or ceiling brackets that securely fasten
boxes in walls or ceilings shall be permitted.
(o) Outlet boxes shall fit closely to openings in combustible walls
and ceilings, and they shall be flush with such surfaces.
(p) Appliances having branch-circuit terminal connections which
operate at temperatures higher than 60 deg. C (140 deg. F) shall have
circuit conductors as described in paragraphs (p) (1) and (2) of this
section:
(1) Branch-circuit conductors having an insulation suitable for the
temperature encountered shall be permitted to run directly to the
appliance.
(2) Conductors having an insulation suitable for the temperature
encountered shall be run from the appliance terminal connections to a
readily accessible outlet box placed at least one foot from the
appliance. These conductors shall be in a suitable raceway which shall
extend for at least 4 feet.
(q) A substantial brace for securing a box, fitting or cabinet shall
be as described in the National Electrical Code, NFPA 70-1993 Article
370-13(d), or the brace, including the fastening mechanism to attach the
brace to the home structure, shall withstand a force of 50 lbs. applied
to the brace at the intended point(s) of attachment for the box in a
direction perpendicular to the surface in which the box is installed.
(r) Outlet boxes shall fit closely to the openings in combustible
wall and ceilings with a maximum of a \1/8\ inch gap. They shall be
flush with the finish surface or project therefrom.
(s) Where the sheathing of NM cable has been cut or damaged and
visual inspection reveals that the conductor and its insulation has not
been damaged, it shall be permitted to repair the cable sheath with
electrical tape which provides equivalent protection to the sheath.
"Cactus Bob" <No_...@me.com> wrote in message
news:Io5b6.2150$Qo5.2...@news.uswest.net...
There is something wrong with having exposed wires in the walls with no
protective covering of any kind. Either this was "not done to Code" or if
it was done to Code, then the Code needs to be tightened up.
Augustaga wrote in message ...