what is the process (ducts, air pumps, etc)
what size would i need (2 & 2.5 ton was recommended)
what is the approximate cost
does anyone know a good & inexpensive service near albany or lake george ny.
is there any brand i should stay away from
anything else?
"hisjr" <his...@verizon.net> wrote in message news:<l14U8.26191$vr5....@nwrddc01.gnilink.net>...
I would caution against an oversized a/c unit. 500-600 sq ft per ton
is adequate particularly where the home is located. Too large of unit
will no run long enough to remove moisture inside the home which can
cause other problems. The constant starting up of the unit even for
shorter periods of time will shorten the life of the compressor as
well.
>> what is the process (ducts, air pumps, etc)
>> what size would i need (2 & 2.5 ton was recommended)
>> what is the approximate cost
>> does anyone know a good & inexpensive service near albany or lake
>> george
> ny.
>> is there any brand i should stay away from
>> anything else?
>
> Two critical factors:
>
> First is the size of the supply duct. Unless your home was originally
> sized for future installation of an A/C unit, the duct will probably
> present too high a back pressure to cool properly. (A/C units
> generally limit air distribution systems to 0.3 in wc max.; whereas
> heating systems allow 0.5 inches of water column max.) Check your
> heating/cooling certificate for which option the manufacture chose for
> your home.
>
> The second is the site location & condition. (The orientation of the
> home is very important. Homes positioned n-s will cool better than
> those positioned e-w.)
Do you mean the length positioned n-s?
>
>
--