Would any one here know of any formulae (not metric) for calculating a
compressor's capacity in tons of cooling with the CFM of the compressor
as a givin?
TIA
This is Turtle.
5 tons ----- 2,000 cfm
4 tons ----- 1,600 cfm
3.5 tons --- 1,400 cfm
3 tons ------ 1,200 cfm
2.5 tons --- 1,000 cfm
2 tons ------ 800 cfm
1.5 tons ---- 600 cfm
TURTLE
Geez, gotta teach you everything......
"Abby Normal" <a_bee_...@spamyahoo.com> , pondered and said :
>Compressor CFM? Please elaborate.
>
Paul
>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~
Please look at http://helpthecritters.com/ , my new domain for helping critters !!!
My personal WWW site is at http://www.pmilligan.net ,
featuring free HVAC, stock market, and other free software
Never color inside the lines in the coloring book.
Color instead where it pleases you to.
You can only color a page once, but there are always more pages.
Isn't this guy asking about CFM compressor displacement rather than CFM
airflow per ton requirements?
"No Freon Going".
"Abby Normal" <a_bee_...@spamyahoo.com> , pondered and said :
>But what if it is NFG, Not Freon, Genetron?
>
"Seaside" <sea...@refrigerationbasics.com> wrote in message
news:q_2O8.11782$Aa4.6...@news0.telusplanet.net...
Thanks,
KD
Yes, you can do it, but it will be different based on the operating conditions.
Most of the confusion here has been focused on the assumption of CFM across the
outside of the coil, etc. It seems he's talking about the compressor
displacement in terms of cubic feet per minute of refrigerant vapor moved by
the compressor INSIDE the system (usually expressed in terms of suction
condition).
So what you need to assume is the condition of the gas entering the compresor.
Typical supermarket conditions assume 65 F superheated gas at the suction inlet
to the compressor, I would expect air conditioning to run a little higher
maybe.
You must find the vapor density of the refrigerant at the suction pressure and
the entering (superheated) temperature on a superheat table. For R-22, for
example, at 20 degrees in the evaporator coil you will get 43 psig, and you
will superheat 45 degrees up to 65 F, so the superheat thermodynamic tables
show the vapor density to be 0.957 lb/cubic foot.
Now that we know the vapor density we can multiply by the CFM of the
compressor. If I push 10 cubic feet/minute X 0.957 lb/cubic foot I will be
moving 9.57 lb/minute of R-22. We also assume at this point that the pounds of
refrigerant flowing through the compressor is equal to the pounds of
refrigerant flowing through the evaporator (and the valve and the condenser
etc.).
Now all I have to do is go back to 20 degrees and multiply by the latent heat -
9.57 lb/minute X 90.5 BTU/lb = 866 BTU/minute or 51,965 BTU/hr - which is the
tonnage for the system at 20 degrees.
If I work the same example at 45 degrees I get a different number. Vapor
density is now 1.587 lb/cubic foot at the compressor inlet, and I'm now moving
15.87 lb/minute at 10 CFM. My tonnage is now the latent at 45 degrees times
the flowrate - 85.7 BTU/lb X 15.87 lb/minute = 1360 BTU/min, or 81,619 BTU/hr.
Easy to do if you have the data. Usually the compressor manufacturer has done
the math for you and they give you a Rating Table for their compressors for
various applications, suction temperatures, etc.
Jim Lavelle
National Refrigerants
www.refrigerants.com
"KoolDood" <can...@zensearch.net> wrote in message
news:3D07F88C...@zensearch.net...
Greetings,
Would any one here know of any formulae (not metric) for calculating a
compressor's capacity in tons of cooling, with the CFM of the compressor as
a givin?
TIA
KD
-----= Posted via Newsfeeds.Com, Uncensored Usenet News =-----
http://www.newsfeeds.com - The #1 Newsgroup Service in the World!
-----== Over 80,000 Newsgroups - 16 Different Servers! =-----
> Your whole question doesn't really make sense, but for the CFM per ton, use
> this rule of thumb: 400CFM per ton of air conditioning.
He means refrigerant circulated. Not air flow.
--
(Actual Compressor Displacement (CFM) divided by the Specific Volume of
Suction Vapor (Cubic feet per pound) multiplied by the Net Refrigeration
Effect (Btu/Lb)= Capacity of Compressor (Btu/Min).
Then you can divide the Btu/Min by 200 to get system tonnage.
The system must be plotted on a PE Chart to obtain the specific Vol. & NRE.