Formula for CFM-Tonnage

606 views
Skip to first unread message

ftwhd

unread,
Jun 12, 2002, 9:55:12 PM6/12/02
to
On Wed, 12 Jun 2002 21:42:36 -0400, KoolDood <can...@zensearch.net>
wrote:

>

If you really want to be KoolDood, please post in plain text not html.
Thanks.

Mike

KoolDood

unread,
Jun 12, 2002, 10:08:59 PM6/12/02
to
Alrighty, is this any better?

Would any one here know of any formulae (not metric) for calculating a
compressor's capacity in tons of cooling with the CFM of the compressor
as a givin?
TIA

HVACFREAK

unread,
Jun 12, 2002, 10:50:36 PM6/12/02
to
use 400 -450 cfm @ ton for heat pump , little less for everything else

TURTLE

unread,
Jun 13, 2002, 1:47:42 AM6/13/02
to

"KoolDood" <can...@zensearch.net> wrote in message
news:3D07FEBB...@zensearch.net...

> Alrighty, is this any better?
>
> Would any one here know of any formulae (not metric) for calculating a
> compressor's capacity in tons of cooling with the CFM of the compressor
> as a givin?
> TIA
>

This is Turtle.

5 tons ----- 2,000 cfm
4 tons ----- 1,600 cfm
3.5 tons --- 1,400 cfm
3 tons ------ 1,200 cfm
2.5 tons --- 1,000 cfm
2 tons ------ 800 cfm
1.5 tons ---- 600 cfm

TURTLE


Abby Normal

unread,
Jun 13, 2002, 2:54:54 AM6/13/02
to
Compressor CFM? Please elaborate.


p...@see_my_sig_for_address.com

unread,
Jun 13, 2002, 3:54:50 AM6/13/02
to
Compressor Freon Movement.

Geez, gotta teach you everything......

"Abby Normal" <a_bee_...@spamyahoo.com> , pondered and said :

>Compressor CFM? Please elaborate.
>


Paul
>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~

Please look at http://helpthecritters.com/ , my new domain for helping critters !!!

My personal WWW site is at http://www.pmilligan.net ,
featuring free HVAC, stock market, and other free software

Never color inside the lines in the coloring book.
Color instead where it pleases you to.
You can only color a page once, but there are always more pages.

Abby Normal

unread,
Jun 13, 2002, 9:13:26 AM6/13/02
to
But what if it is NFG, Not Freon, Genetron?


Seaside

unread,
Jun 13, 2002, 11:36:54 AM6/13/02
to

"KoolDood" <can...@zensearch.net> wrote in message
news:3D07F88C...@zensearch.net...
Greetings,

Would any one here know of any formulae (not metric) for calculating a
compressor's capacity in tons of cooling, with the CFM of the compressor as
a givin?
TIA
KD

Isn't this guy asking about CFM compressor displacement rather than CFM
airflow per ton requirements?


p...@see_my_sig_for_address.com

unread,
Jun 13, 2002, 12:01:20 PM6/13/02
to
NFG means the compressor is not working

"No Freon Going".

"Abby Normal" <a_bee_...@spamyahoo.com> , pondered and said :

>But what if it is NFG, Not Freon, Genetron?
>


profft

unread,
Jun 13, 2002, 4:57:59 PM6/13/02
to
Were not sure exactly what he's asking.

"Seaside" <sea...@refrigerationbasics.com> wrote in message
news:q_2O8.11782$Aa4.6...@news0.telusplanet.net...

KoolDood

unread,
Jun 13, 2002, 5:56:54 PM6/13/02
to
Sorry for the confusion. I have a Carlysle compressor hand book with
all sorts of technical data, but they do not indicate how to identify
the tonnage of the compressor. They do however list the CFM of
refrigerant that is pumped by each model. From that, I was wondering if
it is possible to calculate the size of the compressor in tons.

Thanks,
KD

Allen King

unread,
Jun 13, 2002, 6:44:32 PM6/13/02
to
KoolDood <can...@zensearch.net> wrote in message news:<3D07FEBB...@zensearch.net>...
Hi Kooldood,
Measure the wet bulb and dry bulb temperature drop across the
evaporator coil.
Use Paul Milligan's PM Therm (a free download from his website)to
calculate the enthalpy difference. Apply the enthalpy difference and
supply flow to this formula. BTUH=CFMxenthalpy
differencex4.5
Allen King

Jim Lavelle

unread,
Jun 14, 2002, 1:56:24 PM6/14/02
to
>They do however list the CFM of
>refrigerant that is pumped by each model. From that, I was wondering if
>it is possible to calculate the size of the compressor in tons.
>
>Thanks,
>KD
>

Yes, you can do it, but it will be different based on the operating conditions.


Most of the confusion here has been focused on the assumption of CFM across the
outside of the coil, etc. It seems he's talking about the compressor
displacement in terms of cubic feet per minute of refrigerant vapor moved by
the compressor INSIDE the system (usually expressed in terms of suction
condition).

So what you need to assume is the condition of the gas entering the compresor.
Typical supermarket conditions assume 65 F superheated gas at the suction inlet
to the compressor, I would expect air conditioning to run a little higher
maybe.

You must find the vapor density of the refrigerant at the suction pressure and
the entering (superheated) temperature on a superheat table. For R-22, for
example, at 20 degrees in the evaporator coil you will get 43 psig, and you
will superheat 45 degrees up to 65 F, so the superheat thermodynamic tables
show the vapor density to be 0.957 lb/cubic foot.

Now that we know the vapor density we can multiply by the CFM of the
compressor. If I push 10 cubic feet/minute X 0.957 lb/cubic foot I will be
moving 9.57 lb/minute of R-22. We also assume at this point that the pounds of
refrigerant flowing through the compressor is equal to the pounds of
refrigerant flowing through the evaporator (and the valve and the condenser
etc.).

Now all I have to do is go back to 20 degrees and multiply by the latent heat -
9.57 lb/minute X 90.5 BTU/lb = 866 BTU/minute or 51,965 BTU/hr - which is the
tonnage for the system at 20 degrees.

If I work the same example at 45 degrees I get a different number. Vapor
density is now 1.587 lb/cubic foot at the compressor inlet, and I'm now moving
15.87 lb/minute at 10 CFM. My tonnage is now the latent at 45 degrees times
the flowrate - 85.7 BTU/lb X 15.87 lb/minute = 1360 BTU/min, or 81,619 BTU/hr.

Easy to do if you have the data. Usually the compressor manufacturer has done
the math for you and they give you a Rating Table for their compressors for
various applications, suction temperatures, etc.


Jim Lavelle
National Refrigerants
www.refrigerants.com

Angelo

unread,
Jun 18, 2002, 10:14:32 PM6/18/02
to
Your whole question doesn't really make sense, but for the CFM per ton, use
this rule of thumb: 400CFM per ton of air conditioning.

"KoolDood" <can...@zensearch.net> wrote in message

news:3D07F88C...@zensearch.net...
Greetings,


Would any one here know of any formulae (not metric) for calculating a

compressor's capacity in tons of cooling, with the CFM of the compressor as
a givin?
TIA
KD


-----= Posted via Newsfeeds.Com, Uncensored Usenet News =-----
http://www.newsfeeds.com - The #1 Newsgroup Service in the World!
-----== Over 80,000 Newsgroups - 16 Different Servers! =-----

Bill

unread,
Jun 18, 2002, 11:57:49 PM6/18/02
to
In article <3d0fe...@corp.newsgroups.com>, "Angelo" <apr...@taconic.net>
wrote:

> Your whole question doesn't really make sense, but for the CFM per ton, use
> this rule of thumb: 400CFM per ton of air conditioning.

He means refrigerant circulated. Not air flow.

--

Rick Thompson

unread,
Jun 19, 2002, 12:43:48 AM6/19/02
to
I think what you're looking for is"

(Actual Compressor Displacement (CFM) divided by the Specific Volume of
Suction Vapor (Cubic feet per pound) multiplied by the Net Refrigeration
Effect (Btu/Lb)= Capacity of Compressor (Btu/Min).

Then you can divide the Btu/Min by 200 to get system tonnage.

The system must be plotted on a PE Chart to obtain the specific Vol. & NRE.


Angelo <apr...@taconic.net> wrote in message
news:3d0fe...@corp.newsgroups.com...